Red Lion, Red Lion, Red Lion

Dua Anjing

Member
Join Date
Feb 2008
Location
under the desk looking for a donut...
Posts
435
Hi Guys, We have a Redlion being used as a protocol converter between a Schneider Quantum and Rockwell Micrologix ( I think) . It seems to work OK for a period of time and then it locks up. We can detect from the SCADA that it has locked up because the status we see doesn't make sense. When we look into the PLC's we see that some of the data is getting thru intermittently buut the majority of data is not being updated. Cycling the data on the Redlion usually restores comms. The last two times that we have seen this behavior was after heavy rain. I am not certain but it looks as if the heavy rains cause some form of a fault in the network (multi-mode fibre/ethernet) and oncethis occurs the redlion somehow gets itself into a state that it can't recover from. Currently the comms in the redlion is scheduled to run as often as possible. Any idea's on how to a:) confirm or dispel my suspicions or b:) get the redlion to reset itself once comms has locked up ? Thanks
 
Well, I mean, this solution sounds hokey, but this is what I was thinking initially:

Use a relay to control the power supply to the Red lion if you can get a definitely "fault" signal from the unit, and cycle that relay when you get that fault signal.

However, have you spoken to red lion? Could you have a bad unit?
 
If you do not need the data instantly then I would strongly suggest you set it for a timed up date. One simple way shown to me by Red Lion is to use the Uptick (once per second) to read the data on your comms.

Another item to look at is Gateway blocks. I have used these and they prove to be very efficent. Basically you map the tags from one processor to another. This way you only read what you need to read.

Last trick actually just takes care of the symtoms not the problem. You can create a short program that clears the port just before you request data. This prevents the data que for that port from being overloaded and you only see the most current data.
 

Similar Topics

From the Red Lion website, after some customer enquiries in the last week or so... Rev. March 25, 2024 [18:30] Just thought it might help a...
Replies
9
Views
248
How do you install update on Red Lion Crimson ver 3.1. Do I just need to run the exe file on the host server?
Replies
1
Views
94
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
Replies
4
Views
198
I'm trying to use a Red Lion Cub counter (Cub5B00) as a counter and give the cub's counts to a Graphite G12 PLC/HMI to display. After about an...
Replies
1
Views
104
Hi everybody, I have about three Red Lion HMI's, the calibration on the screens seems correct but where I'm using the pop up keypad to enter...
Replies
1
Views
109
Back
Top Bottom