![]() ![]() ![]() ![]() This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc. |
||
![]() |
![]() |
#1 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 955
|
PLC5 Ethernet sidecar
Can I use a 1785-ENET on a older PLC5-40 that does not support ControlLogix message to enable me to add ControlLogix messaging?
Providing that the firmware on the ENET is new enough. |
![]() |
![]() |
#2 | ||
Member
|
Quote:
Quote:
__________________
|
||
![]() |
![]() |
#3 |
Lifetime Supporting Member + Moderator
|
To reiterate: both the PLC-5 controller and the 1785-ENET need to have firmware that supports CIP/ControlLogix messaging.
The release notes and the Knowledgebase document the minimum revisions for both. |
![]() |
![]() |
#4 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 955
|
OK thanks for that I was hoping that the ENET would allow me to do the messaging, but if not I will need to find another way.
|
![]() |
![]() |
#5 |
Lifetime Supporting Member + Moderator
|
Which model of PLC-5 and which firmware are you using ?
A DH+/EtherNetIP bridge might let you send messages that emulate PLC-5 data tables. Or a Net-ENI equivalent; Real Time Automation might have what you need if the PLC-5 has a serial port. |
![]() |
![]() |
#6 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 955
|
Hi Ken,
Its a 1785-L40E, series D, revision B. I like the idea of using 1756-DHRIO to get comms. This is only a test rig with a 1756-L55, 1756-EN2T connected to a PanelView Plus 7 series B, and the PLC5. I am trying to test the functions of the PvP connected to a stripped down PLC5 and CLX program to avoid using the live system, I have a spare slot that I could put the DHRIO card in and message from the PLC5 into the CLX to do my testing. |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Feb 2014
Location: Stirling, Scotland
Posts: 794
|
If I remember correctly, the PLC5-40E has to have a firmware of series E rev E.2 as a minimum to do CLX messaging.
|
![]() |
![]() |
#8 |
Lifetime Supporting Member + Moderator
|
If you can get a 1756-DHRIO, you might be able to "drill down" from Ethernet to DH+ to that PLC-5.
That was a feature that was absent from RSLinx Enterprise for almost 20 years (RSLinx Classic could do it !), but should work with the newest PV+ terminals and FTLinx. |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 727
|
I don't know if it's helpful, but I had to do a partial upgrade to a system controlled by a non-Ethernet PLC5. We added a CompactLogix 1769-L33ER. It talked via EtherNet/IP to a ControlLogix chassis with a 1756-ENBT and 1756-DHRIO. The -DHRIO was connected to the PLC5. I was able to use pretty simple MSG instructions in the CompactLogix to read/write to the PLC5. I didn't try to do any MSGing from within the PLC5, though. I started to look into it, but decided my time was better spent letting the CompactLogix handle it and document within the PLC5 clearly which registers were coming from the CompactLogix.
|
![]() |
![]() |
#10 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 955
|
I have put a 1756-DHRIO card in my CLX test rack and set up some messages to read the data from my PLC5 test rack and all is working good.
Thank you all. |
![]() |
![]() |
#11 |
Lifetime Supporting Member + Moderator
|
I can endorse the ANC_100e_DH+ comms via ethernet. I have one connected to a cell modem that I move around to remote sites as needed and it has been flawless.
__________________
≈ There are 2 kinds of people in the world... (1) Those that can derive answers from incomplete Data |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
PLC5 PV+ Ethernet limitations | rollie715 | LIVE PLC Questions And Answers | 11 | November 5th, 2009 03:00 PM |
New PC, Dual Ethernet Port Access to Rslinx | SNK | LIVE PLC Questions And Answers | 2 | February 4th, 2009 08:24 PM |
PLC5 Ethernet communication | guidali | LIVE PLC Questions And Answers | 0 | March 23rd, 2007 01:39 PM |
PLC5 (1785-L20E) Ethernet port for programming, while serial port for networking? | flyers | LIVE PLC Questions And Answers | 7 | January 5th, 2007 08:46 PM |
PlC5 Ethernet, a warning, a story, and a question | allscott | LIVE PLC Questions And Answers | 5 | December 8th, 2006 01:05 PM |