PLC5 Ethernet sidecar

Can I use a 1785-ENET on a older PLC5-40 that does not support ControlLogix message to enable me to add ControlLogix messaging?
Providing that the firmware on the ENET is new enough.
  Reply With Quote
Old September 17th, 2023, 06:52 PM   #2
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,826
Quote:
Originally Posted by alan_505 View Post
Can I use a 1785-ENET on a older PLC5-40 that does not support ControlLogix message to enable me to add ControlLogix messaging?
Providing that the firmware on the ENET is new enough.
Quote:
The Ethernet interface module, series A, revision E and later, with a
PLC-5 processor can communicate over Ethernet with ControlLogix
devices or through a ControlLogix Ethernet (1756-ENET) module to
other PLC-5 processors. The following diagram shows an Ethernet
PLC-5 processor (or PLC-5 processor with a 1785-ENET sidecar
module) and the other PLC and SLC processors it can communicate
with using a multihop MSG instruction.
https://literature.rockwellautomatio...m019_-en-p.pdf
__________________
  Reply With Quote
Old September 17th, 2023, 07:12 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,257
To reiterate: both the PLC-5 controller and the 1785-ENET need to have firmware that supports CIP/ControlLogix messaging.

The release notes and the Knowledgebase document the minimum revisions for both.
  Reply With Quote
Old September 17th, 2023, 07:14 PM   #4
alan_505
Lifetime Supporting Member
Australia

alan_505 is online now
 
Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 955
OK thanks for that I was hoping that the ENET would allow me to do the messaging, but if not I will need to find another way.
  Reply With Quote
Old September 17th, 2023, 07:36 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,257
Which model of PLC-5 and which firmware are you using ?

A DH+/EtherNetIP bridge might let you send messages that emulate PLC-5 data tables. Or a Net-ENI equivalent; Real Time Automation might have what you need if the PLC-5 has a serial port.
  Reply With Quote
Old September 17th, 2023, 07:53 PM   #6
alan_505
Lifetime Supporting Member
Australia

alan_505 is online now
 
Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 955
Hi Ken,
Its a 1785-L40E, series D, revision B.

I like the idea of using 1756-DHRIO to get comms.

This is only a test rig with a 1756-L55, 1756-EN2T connected to a PanelView Plus 7 series B, and the PLC5.

I am trying to test the functions of the PvP connected to a stripped down PLC5 and CLX program to avoid using the live system, I have a spare slot that I could put the DHRIO card in and message from the PLC5 into the CLX to do my testing.
  Reply With Quote
Old September 18th, 2023, 03:57 AM   #7
JohnCalderwood
Member
Scotland

JohnCalderwood is offline
 
Join Date: Feb 2014
Location: Stirling, Scotland
Posts: 794
If I remember correctly, the PLC5-40E has to have a firmware of series E rev E.2 as a minimum to do CLX messaging.
  Reply With Quote
Old September 18th, 2023, 06:23 AM   #8
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,257
If you can get a 1756-DHRIO, you might be able to "drill down" from Ethernet to DH+ to that PLC-5.

That was a feature that was absent from RSLinx Enterprise for almost 20 years (RSLinx Classic could do it !), but should work with the newest PV+ terminals and FTLinx.
  Reply With Quote
Old September 18th, 2023, 11:19 AM   #9
joseph_e2
Member
United States

joseph_e2 is online now
 
Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 727
I don't know if it's helpful, but I had to do a partial upgrade to a system controlled by a non-Ethernet PLC5. We added a CompactLogix 1769-L33ER. It talked via EtherNet/IP to a ControlLogix chassis with a 1756-ENBT and 1756-DHRIO. The -DHRIO was connected to the PLC5. I was able to use pretty simple MSG instructions in the CompactLogix to read/write to the PLC5. I didn't try to do any MSGing from within the PLC5, though. I started to look into it, but decided my time was better spent letting the CompactLogix handle it and document within the PLC5 clearly which registers were coming from the CompactLogix.
  Reply With Quote
Old September 18th, 2023, 01:46 PM   #10
alan_505
Lifetime Supporting Member
Australia

alan_505 is online now
 
Join Date: Feb 2007
Location: Melbourne,Victoria,Australia
Posts: 955
I have put a 1756-DHRIO card in my CLX test rack and set up some messages to read the data from my PLC5 test rack and all is working good.

Thank you all.
  Reply With Quote
Old September 18th, 2023, 02:25 PM   #11
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,718
I can endorse the ANC_100e_DH+ comms via ethernet. I have one connected to a cell modem that I move around to remote sites as needed and it has been flawless.
__________________
There are 2 kinds of people in the world... (1) Those that can derive answers from incomplete Data
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC5 PV+ Ethernet limitations rollie715 LIVE PLC Questions And Answers 11 November 5th, 2009 03:00 PM
New PC, Dual Ethernet Port Access to Rslinx SNK LIVE PLC Questions And Answers 2 February 4th, 2009 08:24 PM
PLC5 Ethernet communication guidali LIVE PLC Questions And Answers 0 March 23rd, 2007 01:39 PM
PLC5 (1785-L20E) Ethernet port for programming, while serial port for networking? flyers LIVE PLC Questions And Answers 7 January 5th, 2007 08:46 PM
PlC5 Ethernet, a warning, a story, and a question allscott LIVE PLC Questions And Answers 5 December 8th, 2006 01:05 PM


All times are GMT -4. The time now is 03:34 PM.


.