You are not registered yet. Please click here to register!


 
 
plc storereviewsdownloads
This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc.
 
Try our online PLC Simulator- FREE.  Click here now to try it.

New Here? Please read this important info!!!


Go Back   PLCS.net - Interactive Q & A > PLCS.net - Interactive Q & A > LIVE PLC Questions And Answers

Reply
 
Thread Tools Display Modes
Old September 19th, 2023, 08:43 AM   #1
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 1,021
VFD SLS with no encoder

Hi,
Is there a VFD that can do SLS without an encoder to ANY motor. I know siemens has it but you have to have a special motor from them.
/Tim
  Reply With Quote
Old September 19th, 2023, 09:24 AM   #2
Puddle
Member
United Kingdom

Puddle is offline
 
Join Date: Mar 2022
Location: UK - The Norf
Posts: 246
It's not something I've used, but my G120 course notes say that SLS does not require encoder feedback on the G120. Requires a CU240E-2 F or a CU250S-2 control unit. Will probably also require start drive advanced, safety advanced and it mentions that each axis requires a licence but unsure which specific licence it means.

The only mention of specific motors is this:
"Encoder-less operation is possible for all asynchronous motors and the synchronous motors 1FU8 (SIEMOSYN)"

I looked up 1FU8 and they're all synchronous motors, so I'd take that to mean any asynchronous motor can be used but only that specific synchronous motor.

Siemens also says that the G130 and G150 have the SLS function.
  Reply With Quote
Old September 19th, 2023, 10:38 AM   #3
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 1,021
I read "The use of this safety function without encoder is permitted for asynchronous (induction) motors or synchronous motors of the SIMOTICS A-1FU series (previously: SIEMOSYN)"

https://mall.industry.siemens.com/ma...ducts/10290371
  Reply With Quote
Old September 19th, 2023, 01:50 PM   #4
goghie
Lifetime Supporting Member
Serbia

goghie is offline
 
Join Date: Jan 2008
Location: Belgrade
Posts: 727
Mitsubishi FR-E800-SCE supports SLS without encoder
  Reply With Quote
Old September 19th, 2023, 02:27 PM   #5
Puddle
Member
United Kingdom

Puddle is offline
 
Join Date: Mar 2022
Location: UK - The Norf
Posts: 246
Quote:
Originally Posted by rQx View Post
I read "The use of this safety function without encoder is permitted for asynchronous (induction) motors or synchronous motors of the SIMOTICS A-1FU series (previously: SIEMOSYN)"

https://mall.industry.siemens.com/ma...ducts/10290371
May be worth asking Siemens technical support about this wording if it fits the bill for your project.

I’m reading that as:
-Any asynchronous motor
-Synchronous motors of the 1FU series

But it could well be
-asynchronous motors of the 1FU series
-synchronous motors of the 1FU series

But a quick google only returns results of synchronous motors.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Unusual encoder failure modes ? Ken Roach LIVE PLC Questions And Answers 11 October 22nd, 2015 07:56 AM
Encoder Count Drift marcwand LIVE PLC Questions And Answers 9 March 26th, 2012 02:13 PM
Conveyor movement control using VFD and encoder hhuong LIVE PLC Questions And Answers 6 March 22nd, 2011 02:10 PM
Seimens VFD issue ascot01 LIVE PLC Questions And Answers 5 February 14th, 2009 11:19 PM
Encoder Line in parallel with High Voltage VFD CroCop LIVE PLC Questions And Answers 8 June 26th, 2006 09:05 AM


All times are GMT -4. The time now is 07:35 PM.


.