Redlion Crimson 3.2 now supports CR and Graphite HMIs
Following on from another thread, I just downloaded Crimson 3.2 and it now supports CR and Graphite HMIs.
Time for a 'play' :-) It seems to have successfully opened and upgraded a 3.1 program. The emulator actually works :-) I haven't yet tried to program an actual HMI with it.
__________________
Knowledge is power, share the knowledge. |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
The first one I converted created several errors that I did not expect. It seems to have shifted a couple of things, but they were easily corrected.
Be careful with it! I did upgrade one Graphite to 3.2 successfully so far though and I am looking forward to using that emulator again! |
![]() |
![]() |
#3 | |
Member
![]() ![]() Join Date: Sep 2009
Location: NC
Posts: 907
|
Quote:
|
|
![]() |
![]() |
#4 | |
Member
![]() ![]() Join Date: Feb 2005
Location: Manchester
Posts: 1,916
|
Quote:
![]() I go too excited when the Emulator button was there and the emulator actually started when I pushed the button.
__________________
Knowledge is power, share the knowledge. |
|
![]() |
![]() |
#5 | |
Member
![]() ![]() Join Date: Sep 2009
Location: NC
Posts: 907
|
Quote:
I got a DA70 configuration to download to the Emulator with the Ethernet Port enabled, but it won't collect live data. |
|
![]() |
![]() |
#6 |
Lifetime Supporting Member
|
I never got the Crimson 3.0 emulator to work with Logix5k tags.
I was always able to get it to work with DF1 or Modbus RTU serial protocols as long as I remembered to kill any RSLinx serial drivers first. It also worked with Allen Bradley DF1 Master, DF1 Master via PCCC/EIP, and Modbus TCP (Ethernet) protocols. I don't know if that is relevant to the issues you are having with the 3.2 Emulator. I used my test bench ML1400 for a repair last week, and I don't have any PLCs on the wall I can quickly set up for a test right now. |
![]() |
![]() |
#7 |
Lifetime Supporting Member
|
I just tested the 3.2 emulator communicating DF1 to a Micrologix 1200 using my PC COM1 with a USB to RS232 adapter and it worked fine. I did have to shut down RSLinx first, but that is normal.
|
![]() |
![]() |
#8 | |
Member
![]() ![]() Join Date: Sep 2009
Location: NC
Posts: 907
|
Quote:
Mine is a connection to a Honeywell HC900 using Modbus TCP. Maybe the issue is ethernet because if I disable the ethernet port of the emulator it will load (but obviously with no comms) |
|
![]() |
![]() |
#9 |
Lifetime Supporting Member
|
I need to slap another ML1400 on my test wall and then I can test more protocols including Modbus TCP. In the past, I have seen situations where I had to disable certain Ethernet adapters (wifi for example) in order to get the emulator to work, possibly due to some IP address confusion under the surface where Bill Gate's pet squirrels hang out.
|
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Feb 2005
Location: Manchester
Posts: 1,916
|
Got it working with a Siemens PLC over Ethernet. I noticed that when the emulator started there was no Interface or IP address given on the flash screen. Switched off the emulator, I went in to Link/Options and selected Send to Emulator, then I could Configure the emulator settings, set the Ethernet port 1 to the laptop Ethernet controller. And it worked.
__________________
Knowledge is power, share the knowledge. |
![]() |
![]() |
#11 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 716
|
|
![]() |
![]() |
#12 | |
Member
![]() ![]() Join Date: Sep 2009
Location: NC
Posts: 907
|
Quote:
|
|
![]() |
![]() |
#13 | |
Lifetime Supporting Member
|
Quote:
Are you saying it won't even load the application into the emulated device? |
|
![]() |
![]() |
#14 | |
Member
![]() ![]() Join Date: Sep 2009
Location: NC
Posts: 907
|
Quote:
I'm encouraged that people are getting it to work - that means that there is hope if I can figure out the right combination. |
|
![]() |
![]() |
#15 |
Member
![]() ![]() Join Date: Feb 2005
Location: Manchester
Posts: 1,916
|
I only had a quick 'play' to see if I could get the Comms to work, so I didn't keep notes. I am going to stick with Crimson 3.1 for a least a couple of 3.2 software revisions. I remember that in the Navigation page, Network, I originally had it set to a fixed IP address, I think I changed it to DHCP.
I also switched off wireless, my old laptop used to favour the wired Ethernet, with my newer one I do have to switch off wireless if I ever want to use the wired Ethernet. For a system on a VM I think I would try setting the Ethernet connection to Bridged rather than NAT, that way it would be on the same subnet as the main machine, which should be on the same subnet as the PLC. I would confirm it at the command prompt using the ifconfig command. You might also want to have a quick experiment switching off any antivirus program.