Old September 17th, 2023, 05:22 PM   #1
ganutenator
Lifetime Supporting Member
United States

ganutenator is offline
 
ganutenator's Avatar
 
Join Date: May 2002
Location: kansas
Posts: 1,438
Just the tip

I have PTSD posting here.
But, this thing took awhile to figure out.
When we switched from the Altivar 312 to the ATV320, we had issues w/ the the new drive.
Same application. Same settings.
Since we were a huge customer of Schneider drives, they put their guys on it.
They never did figure it out.
We switched to Toshiba drives.
Then my boss finally figured it out.
He lowered the IR compensation from the default of 100% to 75%.
Been running for months now w/ no issues.
  Reply With Quote
Old September 18th, 2023, 01:49 PM   #2
g.mccormick
Lifetime Supporting Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 925
What was the issue exactly?
  Reply With Quote
Old September 18th, 2023, 02:32 PM   #3
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,715
Yes please - as someone who just despises the plethora of Altivar drives I have because of a low-bid-wins process, I would love to know what you fixed by doing that.
__________________
There are 2 kinds of people in the world... (1) Those that can derive answers from incomplete Data
  Reply With Quote
Old September 18th, 2023, 02:44 PM   #4
ganutenator
Lifetime Supporting Member
United States

ganutenator is offline
 
ganutenator's Avatar
 
Join Date: May 2002
Location: kansas
Posts: 1,438
the issue

When ramping to a stop and immediately changing direction, the Atv 320 would appear to stall and not move.
It was intermittent.
In fact, lower IR compensation to 75% from the default of 100% not only eliminated the the intermittent problem, but it looked smoother as well.
  Reply With Quote
Old September 18th, 2023, 06:20 PM   #5
Jeev
Member
Australia

Jeev is offline
 
Jeev's Avatar
 
Join Date: May 2008
Location: Brisbane
Posts: 670
What was the distance between the drive and motor? Was it a long run?
  Reply With Quote
Old September 18th, 2023, 07:04 PM   #6
ganutenator
Lifetime Supporting Member
United States

ganutenator is offline
 
ganutenator's Avatar
 
Join Date: May 2002
Location: kansas
Posts: 1,438
last reply

Everything worked fine w/ the ATV31, ATV312, Toshiba.
It was the change to the ATV320.
Just passing on the tip.
over and out.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
CO2 snuffing system for flare tip shkoko2000 LIVE PLC Questions And Answers 3 October 15th, 2020 06:10 AM
Fanuc Robot Tip change patelaksh30 LIVE PLC Questions And Answers 6 March 25th, 2018 02:28 PM
Programming tip require for RS Logics 500. AB2005 LIVE PLC Questions And Answers 3 October 22nd, 2013 04:18 AM
Tip Stuck Countermeasure Question zai_jnr LIVE PLC Questions And Answers 4 November 13th, 2009 08:26 PM


All times are GMT -4. The time now is 08:01 PM.


.