Shelf maintenance for VFDs ?
This is a little OT, but I know there are some experts here on the forum with the relevant experience.
I have a project that expects a very long lifespan from PowerFlex 70 VFDs. To insure them against inevitable obsolescence, I would like to buy a few and have them available in our stock as replacements. But I know that capacitors get cranky if left on the shelf for years. I don't do enough VFD repair to be capable of doing capacitor reformation on these little 1/2 HP drives. I was thinking of basically automating my storage: I have a disused cabinet with an old MicroLogix and a 480V contactor. I could have the MicroLogix power those drives up once every few months, read their serial numbers and runtime hours, then send me an e-mail to remind me that they've done so. If you did that, how often would you power up those drives ? Every 3 months ? 6 ? 12 ? |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Dec 2012
Location: Bathurst
Posts: 9
|
If you speak to a Rockwell drive expert they will tell you how to setup a DC voltage to reform the capacitors. I asked about this in the past and that was the general answer but I cant remember the details.
|
![]() |
![]() |
#3 | |
Lifetime Supporting Member + Moderator
|
This what Siemens says for their VFDs:
Quote:
__________________
Jesper ![]() NOTICE: JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm ! Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ |
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Mar 2010
Location: casablanca
Posts: 654
|
In page 3 of this document,you can find the reforming capacitors recommendations
Preventive Maintenance Checklist of Industrial Control and Drive System Equipment https://literature.rockwellautomatio...d001_-en-p.pdf
__________________
Optimist will tell you the glass is half-full; the pessimist, half-empty; and the engineer will tell you the glass is twice the size it needs to be Last edited by tarik1978; September 18th, 2023 at 05:58 AM. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Mar 2005
Location: Midwest
Posts: 15
|
There was a Rockwell webinar around January 2021. I'm not sure if these can be looked up later on. The title was "AC Drive Best Practices."
This is what I wrote about reforming: • Reforming capacitor guidelines/recommendations ○ <1 year stored as rated - no reforming required ○ 1 - 2 years: apply rated voltage as normal for 60 min w/o load ○ 2 - 3 years: connect DC power supply directly to DC terminals, ramp up voltage from 0-100% of DC bus voltage in steps of 25%, under no load. Dwell at 25, 50, 75% for 30 minutes each, dwell at 100% for 60 minutes. ○ >3 years: apply DC power supply as above but dwell at each step for 120 minutes ○ DC bus voltage: 325 VDC on 230V input drive, 680 VDC on 400/480V drive, 848 VDC on 600V drive |
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Oct 2022
Location: NH
Posts: 20
|
You can also use a regular single-phase AC XFMR going up in 25% increments(different taps) connected to just two of the L terminals. The rectifier bridge doesn't care one bit about lower voltages or what "Lx" the voltage is coming from. It would care if it were a 230V vs 480V. Just take care on that matter.
No way I'm buying a 1000V adjustable DC power supply. Last edited by LegacyLee; September 18th, 2023 at 12:00 PM. |
![]() |
![]() |
#7 | |
Member
![]() ![]() Join Date: Mar 2005
Location: Midwest
Posts: 15
|
Quote:
https://www.rockwellautomation.com/e...allations.html |
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Best strategy to isolate conveyer for maintenance? | Tronador | LIVE PLC Questions And Answers | 5 | April 1st, 2020 06:01 AM |
The urgent need around the country for Maintenance Technicians-What works for you ? | Cydog | LIVE PLC Questions And Answers | 46 | January 24th, 2020 03:24 PM |
Distinguishing Real vs. Maintenance Alarms | JoshM | LIVE PLC Questions And Answers | 7 | May 1st, 2012 01:18 PM |
Managing Maintenance People | Rob S. | LIVE PLC Questions And Answers | 12 | April 2nd, 2011 11:05 PM |
Indicating maintenance status in HMIs. | RMA | LIVE PLC Questions And Answers | 21 | February 3rd, 2006 07:49 AM |