Shelf maintenance for VFDs ?

This is a little OT, but I know there are some experts here on the forum with the relevant experience.

I have a project that expects a very long lifespan from PowerFlex 70 VFDs. To insure them against inevitable obsolescence, I would like to buy a few and have them available in our stock as replacements.

But I know that capacitors get cranky if left on the shelf for years. I don't do enough VFD repair to be capable of doing capacitor reformation on these little 1/2 HP drives.

I was thinking of basically automating my storage: I have a disused cabinet with an old MicroLogix and a 480V contactor. I could have the MicroLogix power those drives up once every few months, read their serial numbers and runtime hours, then send me an e-mail to remind me that they've done so.

If you did that, how often would you power up those drives ? Every 3 months ? 6 ? 12 ?
  Reply With Quote
Old September 18th, 2023, 03:40 AM   #2
Puddle
Member
United Kingdom

Puddle is offline
 
Join Date: Mar 2022
Location: UK - The Norf
Posts: 246
It really depends what type of capacitor is used, but I'd have thought 12 months should be fine. Although if you're going to the effort of automating it you might as well have it fire up monthly. A place I used to work had an electrician wire up and test all spare drives on a monthly basis after they once had a replacement fail and cause production issues.

This is actually a pretty big issue with the original Xbox. The system clock was maintained by a capacitor and now that a lot of the consoles aren't used a lot, they've been known to leak and cause damage to the motherboard.
  Reply With Quote
Old September 18th, 2023, 01:25 PM   #3
I_Automation
Lifetime Supporting Member
United States

I_Automation is online now
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,385
The VFD's with this spec listed that I have seen have all said 12 months to stop the capacitors from degrading.


Plus I think some said to build the incoming power, not just apply 240 or 480, but start at 100V and build slowly to line voltage over 12 to 24 hours
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Old September 18th, 2023, 01:30 PM   #4
g.mccormick
Lifetime Supporting Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 925
Ken. For some reason your post was created twice.

If you are going through the steps of automating it, you may as well just have them power up for an hour or so every two or three months.

Every few months will keep the capacitor smoke happy, but is not so often that you are going to realistically wear out the precharge circuits.
  Reply With Quote
Old September 18th, 2023, 02:21 PM   #5
TheWaterboy
Lifetime Supporting Member + Moderator
United States

TheWaterboy is offline
 
TheWaterboy's Avatar
 
Join Date: May 2006
Location: State of Denial
Posts: 1,715
I think a ramp up is a better option in any case. I have some stock that I only pull when I need one, I'll take a half a day and charge them up incrementally over several hours.

Bear in mind that since they will only need minimal current so you can get away with a 120Vx480V XFMR with a series resistor for inrush protection and they will charge up just fine.
__________________
There are 2 kinds of people in the world... (1) Those that can derive answers from incomplete Data
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Best strategy to isolate conveyer for maintenance? Tronador LIVE PLC Questions And Answers 5 April 1st, 2020 06:01 AM
The urgent need around the country for Maintenance Technicians-What works for you ? Cydog LIVE PLC Questions And Answers 46 January 24th, 2020 03:24 PM
Distinguishing Real vs. Maintenance Alarms JoshM LIVE PLC Questions And Answers 7 May 1st, 2012 01:18 PM
Managing Maintenance People Rob S. LIVE PLC Questions And Answers 12 April 2nd, 2011 11:05 PM
Indicating maintenance status in HMIs. RMA LIVE PLC Questions And Answers 21 February 3rd, 2006 07:49 AM


All times are GMT -4. The time now is 08:38 PM.


.