![]() ![]() ![]() ![]() This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc. |
||
![]() |
![]() |
#1 |
Lifetime Supporting Member
![]() ![]() Join Date: Oct 2010
Location: Trelleborg
Posts: 1,021
|
VFD SLS with no encoder
Hi,
Is there a VFD that can do SLS without an encoder to ANY motor. I know siemens has it but you have to have a special motor from them. /Tim |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Mar 2022
Location: UK - The Norf
Posts: 249
|
It's not something I've used, but my G120 course notes say that SLS does not require encoder feedback on the G120. Requires a CU240E-2 F or a CU250S-2 control unit. Will probably also require start drive advanced, safety advanced and it mentions that each axis requires a licence but unsure which specific licence it means.
The only mention of specific motors is this: "Encoder-less operation is possible for all asynchronous motors and the synchronous motors 1FU8 (SIEMOSYN)" I looked up 1FU8 and they're all synchronous motors, so I'd take that to mean any asynchronous motor can be used but only that specific synchronous motor. Siemens also says that the G130 and G150 have the SLS function. |
![]() |
![]() |
#3 |
Lifetime Supporting Member
![]() ![]() Join Date: Oct 2010
Location: Trelleborg
Posts: 1,021
|
I read "The use of this safety function without encoder is permitted for asynchronous (induction) motors or synchronous motors of the SIMOTICS A-1FU series (previously: SIEMOSYN)"
https://mall.industry.siemens.com/ma...ducts/10290371 |
![]() |
![]() |
#4 |
Lifetime Supporting Member
![]() ![]() Join Date: Jan 2008
Location: Belgrade
Posts: 728
|
Mitsubishi FR-E800-SCE supports SLS without encoder
|
![]() |
![]() |
#5 | |
Member
![]() ![]() Join Date: Mar 2022
Location: UK - The Norf
Posts: 249
|
Quote:
Im reading that as: -Any asynchronous motor -Synchronous motors of the 1FU series But it could well be -asynchronous motors of the 1FU series -synchronous motors of the 1FU series But a quick google only returns results of synchronous motors. |
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Unusual encoder failure modes ? | Ken Roach | LIVE PLC Questions And Answers | 11 | October 22nd, 2015 07:56 AM |
Encoder Count Drift | marcwand | LIVE PLC Questions And Answers | 9 | March 26th, 2012 02:13 PM |
Conveyor movement control using VFD and encoder | hhuong | LIVE PLC Questions And Answers | 6 | March 22nd, 2011 02:10 PM |
Seimens VFD issue | ascot01 | LIVE PLC Questions And Answers | 5 | February 14th, 2009 11:19 PM |
Encoder Line in parallel with High Voltage VFD | CroCop | LIVE PLC Questions And Answers | 8 | June 26th, 2006 09:05 AM |