HI All,

I have to use thermocouple (sine the give voltage as output), and I have two analog inputs in my TM221CE16R, which are voltage dependent (0-10v, with LSB of 10mV). How can I do that? I guess I cant do this directly, does anyone know of any reliable, but a bit cheap amplifiers for Thermocouples? The other option is to but the extra cartridge for thermocouples by Schneider Electric.

Any suggestion?

Thanks.
 
Look at how little voltage a thermocouple produces (approximate values):

Type K 0 to 1200 Deg C = 0 to 48.8mV, 1 Deg C change ranges from approx 0.039mV to 0.034mV
Type J 0 to 1200 Deg C = 0 to 69.5mV, 1 Deg C change ranges from approx 0.050mV to 0.057mV
Type T 0 to 400 Deg C = 0 to 20.8mV, 1 Deg C change ranges from approx 0.039mV to 0.062mV

A 0 to 10Vdc input does not have enough resolution to handle is too such small changes as 0.034mV (0.000034V)/deg. That's 10.0V/0.000034 = 294,117 parts of resolution = 100 0111 1100 1110 0110 which would require a 19 bit A/D converter to resolve a 1 degree C change in K type thermocouple, assuming no noise

The suggested alternative is to use a temperature transmitter which produces a 0-10Vdc output proportional to a scaled temperature input.

Be alert to the fact that a configuration tool for scaling the temperature (0-100 Deg? 200-400 Deg C? 0-1500 Deg C?) over the range of the output (0-10V) requires some means - keyboard and display, PC with Modem and software, HART communicator, all of which cost something.

If you're not will to spend money on a configuration tool, look for a vendor that sells a transmitter pre-configured to the range you need, or who will configure it for you for some nominal fee.

Also be aware that a grounded thermocouple with a non-isolated transmitter can create a ground loop the looks like a tempeature offset.

My suggestion is to always buy 'ungrounded' thermocouple assembly.
 
Look at how little voltage a thermocouple produces (approximate values):

Type K 0 to 1200 Deg C = 0 to 48.8mV, 1 Deg C change ranges from approx 0.039mV to 0.034mV
Type J 0 to 1200 Deg C = 0 to 69.5mV, 1 Deg C change ranges from approx 0.050mV to 0.057mV
Type T 0 to 400 Deg C = 0 to 20.8mV, 1 Deg C change ranges from approx 0.039mV to 0.062mV

A 0 to 10Vdc input does not have enough resolution to handle is too such small changes as 0.034mV (0.000034V)/deg. That's 10.0V/0.000034 = 294,117 parts of resolution = 100 0111 1100 1110 0110 which would require a 19 bit A/D converter to resolve a 1 degree C change in K type thermocouple, assuming no noise

The suggested alternative is to use a temperature transmitter which produces a 0-10Vdc output proportional to a scaled temperature input.

Be alert to the fact that a configuration tool for scaling the temperature (0-100 Deg? 200-400 Deg C? 0-1500 Deg C?) over the range of the output (0-10V) requires some means - keyboard and display, PC with Modem and software, HART communicator, all of which cost something.

If you're not will to spend money on a configuration tool, look for a vendor that sells a transmitter pre-configured to the range you need, or who will configure it for you for some nominal fee.

Also be aware that a grounded thermocouple with a non-isolated transmitter can create a ground loop the looks like a tempeature offset.

My suggestion is to always buy 'ungrounded' thermocouple assembly.

you are righ on spot..I feel that using an RTD or thermocouple with the temperature input module(which I have to but extra) of my PLC will be the best option.
 

Similar Topics

Hello everyone, I'm working on a project that involves controlling an array of nozzles within a CNC environment, where the nozzles travel along a...
Replies
5
Views
118
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
Replies
4
Views
124
Hi, Seeking consultation on an implementation matter, and have a question about Modicon Compact 984 communication through RS485: Three Modicon...
Replies
3
Views
82
Dear all, I don't know why setup of password became challenging and weird. After setting up the password and try to upload the ladder from the plc...
Replies
3
Views
91
Dear All, I need a sample PLC program to count the output pulse of a mass flow meter so that a specific amount of mass (for example 100gm)can be...
Replies
2
Views
79
Back
Top Bottom