Hi Everyone,

Good day! Can anyone help us with our Com'X 510 to connect in our Archestra System Platform. How or what else do we need to do. Our Com'X510 is the master of ION6200. We need to get the data of ION6200 to Com'X510 from our Server.

Thanks in advance,
Joe
 
Look at page 62 of the manual:

Accessing the Internal Modbus Slave Device

The internal Modbus TCP server allows reading the digital input and analog input
values of the Com’X via various Modbus registers . These registers can be read
using Modbus slave ID 255.
After you configure the Com’X inputs in Device Settings, values are accessible
through the gateway. The register values can also be viewed in the
Measurements Table tab for measurements selected for logging.
The internal Modbus TCP server is active when Modbus TCP/IP communications
is enabled in Firewall Management.
 

Similar Topics

Hi! I am using an M200 PLC connected by Modbus TCP/IP with a Com'X 510 energy server. I need to read the data corresponding to the voltage of a...
Replies
0
Views
1,011
Hi to all :), Can I ask how to connect ION6200 Powermeter to Com'X510 because we try to follow the instruction on the manual but no luck. Have...
Replies
1
Views
1,691
I'm retrofitting equipment, but I didn't want to change the electrical characteristics of the panel. In this equipment I have a dedicated...
Replies
0
Views
61
Hi folks ! Got an older Modicom BM85 and I suspect that it's not passing data to ModBus+ network. We had a power loss for a few days and I suspect...
Replies
0
Views
59
I need to recommend a PC to replace a customer's old Windows 7 computer. The only thing I need to think through is the serial com port to...
Replies
21
Views
640
Back
Top Bottom