ABB ACS550 Earth Fault

I just replaced this drive as the old one went out when the plant had a power surge/flicker.

1-Installed the drive
2-Powered up
3- Got an immediate EARTH FAULT, so I check the manual and it talks about wires being grounded.
4- Disconnected wires from the motor and ohm out the wires to ground( CHECKS GOOD)
5-So I ohmed out the motor and I was getting 40-50 ohms when tested to ground.

6-I have not powered up the drive with out the wires disconnected. I will try that next to confirm my thoughts that the motor windings are starting to go bad and current is leaking out.

Bad motor?
  Reply With Quote
Unread December 2nd, 2019, 02:06 PM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is online now
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,329
Quote:
Originally Posted by Leukic View Post
5-So I ohmed out the motor and I was getting 40-50 ohms when tested to ground.

Bad motor?
Yes. Less than 10kohms is failing. Some drives require much more than that to overcome a ground fault.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Unread December 2nd, 2019, 02:49 PM   #3
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 81
Seperated motor from power booted drive up and no fault. looks like im searching for a motor. Thanks OkiePc
  Reply With Quote
Unread December 2nd, 2019, 08:38 PM   #4
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,848
VFDs are better at finding faults than a lot of other things that are supposed to...
  Reply With Quote
Unread December 3rd, 2019, 08:02 AM   #5
OkiePC
Lifetime Supporting Member
United States

OkiePC is online now
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,329
Quote:
Originally Posted by OkiePC View Post
Yes. Less than 10kohms is failing. Some drives require much more than that to overcome a ground fault.

That should read 10 megohms. I have seen motors on starters work as low as 2 Mohm. I once replaced an obsolete 1336 VFD with a Toshiba G7 and it wouldn't run. The motor megger test showed 80 Megohms to ground... The 1336 was fine with it, the G7 said nope.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Abb acs550 pfc macro control osama223 LIVE PLC Questions And Answers 2 August 1st, 2017 10:51 AM
ABB AC drive fault mmgch LIVE PLC Questions And Answers 3 August 7th, 2009 04:48 AM
Generic fault finding methodology Engineer1 LIVE PLC Questions And Answers 7 July 16th, 2009 08:36 PM
RSLogix User Fault Routine jthornton LIVE PLC Questions And Answers 17 October 23rd, 2008 03:55 PM
Mitsubishi Still Sucks... Eric Nelson LIVE PLC Questions And Answers 23 January 15th, 2003 05:15 PM


All times are GMT -5. The time now is 05:12 PM.


.