Dear all
Can anybody help me for S7 200 Analog Output
My Problem is , In Catlog the type of inbuilt Analog output (224XP Cpu)is +/-10V or 0 - 20 mA.I require -10V to +10V .As i force 32000 from Microwin 4.0 to analog output there is 10 V output fine,but as i force -32000 thre is 0V output at the output.Please point where i am wrong?
Nehe
 
Last edited:
Inbuilt analog output of CPU is designed to give just 0 to +10V from 0 to 32000 counts.
-32000 won't give you -10v from CPU AO
If you want 0-(-10v)then go for EM modules or DC/DC converter.

OK give a try by changing the polarity of your wires from analog output.
 
Last edited: