I am using S7-300 PLC with 315 2DP CPU.
We have connected K type Thermocouple to analog I/P module, . I have defined same in the hardware configuration. Please let me know the count range (software), and temperature range for K type thermocouple.
 
Hello gujuraj;

From the Siemens manual "S7-300 module data"

TC_K_S7-300.jpg


Hope this helps,
Daniel Chartier
 
As a side note, "I/P" is most often used to designate a current to pneumatic trransducer. This device, often used in process control, converts a 4-20 mA signal to a 3-15 psig signal for valve positioning.

I have noticed a number of posts lately using I/P and O/P for input and output respectively. I'm not sure where this is coming from, but as a personal opinion I'd rather see the words spelled out for clarity.
 

Similar Topics

I have a fair amount of Logix and Studio experience, but this is my first project with Studio v33 and a 5069 CPU and -IY4 card. The processor is...
Replies
3
Views
1,130
Is it possible to wire a J type Thermocouple directly to a Allan Bradley Analog input card, specifically a 1769-IF4 card, and scale the reading to...
Replies
8
Views
2,516
Hay everyone, I am using a Micrologix 1400 with 1762SC-IF8 module to read temperature from different parts of a plastic extrusion line. I am...
Replies
5
Views
2,294
Hi Friends, A quick one please. Can online changing of Thermocouple Type K to J (configuration change in 1769 IT6/A module) fault compactLogix...
Replies
11
Views
3,735
Hello All, My name is Austen, and I am working on a project for a plastics extrusion plant that deals with a lot of thermocouples and other...
Replies
6
Views
2,103
Back
Top Bottom