Silo fill measurements with strain gauges.

JesperMP

Lifetime Supporting Member + Moderator
Join Date
Feb 2003
Location
ᚴᚬᛒᛅᚾᚼᚬᚠᚾ
Posts
16,292
Hi all.

I have a project with individual silos (100 t capacity each), and am thinking about using strain gauges for the fill level measurement.

1. It does not have to be super accurate. +/- 5% is plenty good. The silos stand with their own individual legs. Should I measure on one leg, several legs, or all legs ?

2. Should I use a single strain gauge foil on each leg, or should I on each leg arrange 4 foils in a bridge arrangement ?
2a. I can only find strain gauge foils with a single strain gauge. Does there exist foils with 4 strain gauges pre-configured in a bridge connection ?
(I have a lot of experience with load cells, where you always use bridge connections, but I have no experience with strain gauges).

3. I can find strain gauges of steel or aluminium. Why would I chose one over the other ?

4. Any good suppliers in the EU ?

5. Any other useful tips or links to good sites about strain gauges ?

Thanks in advance.

edit:

6. What about the physical wire connections on the strain gauges ? What do people do ?
I am thinking about cutting the bottom of a regular terminal box and place it over the strain gauge(s), and also place a DIN rail for the further connection or even place the converter directly in the box.
 
Last edited:
I have found strain gauges are better at measuring stretch than compression. Why do you not want to just use load cells?
 
True a strain gauge is supposed to be "bolt on" but bear in mind that its accuracy is very hard to predict. Unlike a load cell your actual deflection is going to be unknown until you attach the sensor to the beam. You will have to experiment a good bit to find a good location on your frame to place the strain gauges. Make sure there are no frame cross supports going around your strain gauge as this will really throw your readings.

Also one thing I learned the hard way. Attach you strain gauge with the silo full. Strain gauges are designed to measure stretch not compression.

Also on the very bottom end where the silo is almost empty you may see a deadband where the weight is not enough to cause any measurable compression of the beam.
 
I dont need the accuracy. I will do a simple full-empty calibration and be done with it.
It will just show 0-100% on the HMI.
I am aware about the installation constraints.

Thanks for the tip regarding gluing the sensor with the silo full.
 

Similar Topics

I have been working on this since yesterday. I have some college technical training and I am trying to teach myself plc's for work. I have become...
Replies
9
Views
3,276
Customer does not want any silo penetrations. Hates level sensors on top of silos. No capacitance sensors either. Would be great if it had...
Replies
6
Views
1,502
I am looking for a way to determine level in a silo. The material is called Perilite which has a very light density. Bulk density could be...
Replies
10
Views
2,740
Hi, i have a problem with measuring level in silo using siemens S7-1200. On top of the silo there is an 0-10V radar level sensor, it works...
Replies
14
Views
3,619
I am working with plc5. I am using the CPT function but getting errors. The level of the silo is inputed at F51:031. The silo cuft is 3393 with...
Replies
3
Views
1,572
Back
Top Bottom