struggling getting the firmware update on this controller. new build, assigned an IP via bootp, can ping it, but i get a not in the proper mode error. it is in program mode. any suggestions?

fail.jpg
 
I have always did it via USB, doesn't the IP address get wiped out during the upgrade?
same result when attempting to do it via usb.

from reading around someone was saying they left bootp up and running to 'perserve' the address. didnt work for me.
 
You are browsing too far into the tree when trying to flash the firmware. Don't browse through the bus, select the first level item under the Ethernet I/P driver.
 
Yup; the first CPU object in the browsing tree should be highlighted, not the "down through the backplane to the CPU" object.


The old ControlLogix had modular Ethernet so you had to go through such a route, but not the modern ones with a built-in Ethernet port.

In my opinion RSLinx and/or ControlFlash should do a better job of detecting and notifying users of such a path problem.
 
You are browsing too far into the tree when trying to flash the firmware. Don't browse through the bus, select the first level item under the Ethernet I/P driver.

Yup; the first CPU object in the browsing tree should be highlighted, not the "down through the backplane to the CPU" object.


The old ControlLogix had modular Ethernet so you had to go through such a route, but not the modern ones with a built-in Ethernet port.

In my opinion RSLinx and/or ControlFlash should do a better job of detecting and notifying users of such a path problem.

šŸ™ƒ

thank you gentlemen.
 
I have always did it via USB, doesn't the IP address get wiped out during the upgrade?

No the flashing only updates the CPU card and not the Ethernet card so all the Ethernet settings stay the same, I think the only time you see Ethernet updates are with series updates
 

Similar Topics

I'm in the process of installing a new 1769-L30ER controller as a retrofit to a 1794-L34. I'm trying to find out if I can load the firmware and...
Replies
1
Views
629
Good morning everyone. I have a situation that is really stumping me. I have three separate but identical machines, all running 1769-L30ER PLCs...
Replies
11
Views
3,501
Good afternoon. I have an issue that I have never encountered before and am uncertain of where to start. I have three machines, all with...
Replies
0
Views
943
Hey everyone, I am trying to message to a IndraControl L45 controller that I do not have access too. I have been given given a list of addresses...
Replies
3
Views
1,325
Hello Friends I need to replace a Micrologix 1400 L32BWA with 1 1762-OB16. I had thought in a 1769-L30ER, 1 1769-IQ32 and 2 1769-OW16. But...
Replies
3
Views
2,383
Back
Top Bottom