Ok, so I created a new generic analog input faceplate for a new 0-4000 psi pressure transmitter we have at our plant. After configuring the correct tag and PLC, the display is showing a signal failure. The pressure value displayed is correct and matches the actual pressure we are reading in the vessel. Confirmed this with calibrated gauges. Looking at the Function block routine shows that the "srcq" parameter within the AOI has a value of 32. We cant really find what is out of range, or what NaN means. Also unclear about an invalid combination. Anyone that can shed some light and point in the right direction would be much appreciated. Thanks. Factory Talk View ver. 8.20.00
 
When you say "display is showing a signal failure", are speaking of the faceplate or an Icon? Did you create your own Icon too, or are just showing a value?
NaN means Not a Number.
I've never rolled my own faceplate with PlantPax, too much work. Maybe someone else can pitch in.
 
I mis-understood, you are using the Basic AI block and faceplate. When you said created, I thought you rolled your own.

In the function block what do you have connected to Inp_PVBad? Should be wired to the channel bad status.
 
Identical AOI but we aren't using any fault tags at the moment. I tried just writing a constant 0 to both input pins, but still same result. I replaced them with tags that will be used in the future, with "0" values currently and the SRCQ parameter changed to "1". The faceplate, however is still showing a signal failure.
 
check the "Cfg_FailHiLim" setting. It's default is 103.9583 and it will show "Signal Failure" if the value is higher.


It's also on the Faceplate where you set the alarm setpoints.
 
check the "Cfg_FailHiLim" setting. It's default is 103.9583 and it will show "Signal Failure" if the value is higher.


It's also on the Faceplate where you set the alarm setpoints.


Yeah, that is set to 4100. Actual signal is about 1052.00 or so during normal condition. Whats weird, is that we have another FB routine with identical code looking at a Temperature sensor. It is functioning correctly with no signal failure. Actual value is within all the limits just like the non-functioning routine. Im sure its probably a missed parameter somewhere, just frustrating. LOL
 

Similar Topics

Hey all Im still a newbie so i need a little help. I simply want to make an expression that kan change the text of an header depending on which...
Replies
2
Views
1,674
Hello All We have 3rd party vendors that run on older versions of PLC (Plc2.0) while we run the main system using plantpax and PLC 3.5-10. Plantpx...
Replies
0
Views
50
Dear Members, Hello, we are working on a project and facing an issue with the plantpax 5 PMTR library, we have a bidirectional motor, which has 2...
Replies
6
Views
189
The PMTR has a timeout parameter for run feedback during a start, but once the motor has been running for a while and loses that run feedback (to...
Replies
0
Views
195
Hello, I am upgrading some custom AOI's for a customer that was using plantpax 3.5 they are moving to Pax v5. In their old AOI's they were...
Replies
0
Views
499
Back
Top Bottom