Hi guys,
Currently on a job. Trying to get a card to connect. An issue we believe is the solution is to change the cards general settings from rack optimisation. But the issue we have is it is only allow us to select rack optimisation doesn’t display any other options. Does anyone have any idea maybe why? The card is a
1734-AENTR/B Revision 5. Any information would be greatly appreciated.

Thanks

PLC Apprentice
 
What exact part number of POINT I/O module are you using ? What problem are you experiencing that makes you want to change the connection type.

You're correct that you can generally configure a discrete POINT I/O module in a 1734-AENT(R) adapter to be part of the Rack Optimized connection, or to have its own Module type connection with its own RPI and its own Configuration and Status data.

When I open the Module Definition for a discrete module in a 1734-AENT(R) adapter, I get a pull-down for the Connection with options of Data, Listen-Only, and Rack Optimization.

As far as I know, you can't make this change online with 1734 modules.
 

Similar Topics

I've blown the Output Transistor on the Output Card of a Compact Logix 1769-L24ER-QBFC1B It says J378. Does anyone know the replacement part...
Replies
3
Views
198
An issue occurred at an organization here in whereby the ControlNet card developed a fault. Card Details: Catalog/Series; 1756-CN2RXT B Part No...
Replies
0
Views
436
I have a project where I will need around 20 IO cards. I'll probably have 5 on a compactlogix L320ER and 15 or 20 on a Point IO AENTR module. The...
Replies
4
Views
970
Are any of you guys out there aware of a consolidated list of I/O cards that can be replaced online? We just replaced a 1756-IF16 card while the...
Replies
2
Views
1,521
I have a system that is using TCP sockets. There are 5 connections between the Ethernet card and the end devices (smart conveying system)...
Replies
0
Views
698
Back
Top Bottom