Step 7 output value scaling

Sake_no_oni

Member
Join Date
Jan 2013
Location
Dnipropetrovsk
Posts
18
Dear All,

I’m using S7-300. I need to scale an output value for a valve open control. I have an I/O field on my SCADA (WinCC v6.0) where an operator inputs value between 0% and 100%, which is the percent of the valve open, 0% for 4 mA and 100% for 20 mA. I’ve tried to use FC105 and FC106, but in both cases I have 0 on the OUT. I’ve also tried to write the formula from these functions’ “help” manually, but the result was same (zero on the “out”). I’d like to know what I am doing wrong.

Thanks in advance and Best Regards!
 
With your analog output set to 4-20ma (check your module parameters - double click the module in hardware config)
4-20ma= 0-27648
 