RSLinx Enterprise & RSLinx Classic serial port conflict

caleno

Member
Join Date
Mar 2010
Location
NJ
Posts
36
Hi,

I have successfully interfaced a Micrologix 1400 and my panelview 1000. In the process I used the RS-232 DF1 driver/port to communicate with the PLC. Ethernet to communicate with the PV 1000. At some point I had to disconnect RSLinx Classic so that RSLinx Enterprise could communicate with the PLC as well.

o_O The problem I have is that I need to go back to RSLinx Classic, so I can edit the PLC code. But RSLinx Enterprise is still using (Mode: Online) the RS-232 DF1 driver. How do I stop/prevent RSLinx Enterprise from using the driver OR how can I use my RSClassic without this Serial port conflict?

Thank you,
 
I assume you're speaking of the PC that you're doing development with.

Kill the RXLinx Enterprise process using the task manager.

OR

Why not but a simple ethernet switch between the PLC & HMI and connect your PC to it also using the its ethernet port. I always carry with me a small switch that I can insert in small standalone systems that don't have a switch so that I can have fast comms and avoid scenarios like you describe.
 
jstolaruk, thanks so much for your reply. I knew I should have used an ethernet switch to ease communications. Anyways, i followed your suggestion and the PLC & Panelview are communicating and I still can go online on the computer with the PLC. Perfect!

I am still however, having trouble with the conflicting ports. Using the Task Manager on the computer to turn off RSLinx Enterprise does not work...RSLinx E. is not there. Any other suggestions? I deleted the RS-232 DF1 driver from RSLinx Enterprise communications windows on FTV.
 
No, and I just had this scenario a week or so ago and didn't run in to it. The only thing I can think of is to reboot the pc, startup rslinx and connect using the serial port to the processor with rslogix Then start factory talk view studio.
 
jstolaruk, I found the answer to Stop RSLinx Enterprise Service:
1. Go to Control Panel-> Administrative Tools-> Services.
2. Double-click on RSLinx Enterprise and on the left side of screen click on "Stop" the service.
3. The same procedure can be used to "Start" it.
 
Once you get RSLinx E stopped you might still get a port conflict message. If you do go into device manager and disable then re-enable the com port. Window sometimes likes to keep an association even though the software has stopped running (especially when it’s a service like RSL. E.). Disabling the com port breaks the association and frees up the port.
 

Similar Topics

Hi All, Looking for some clarity regards the relatively recent rebranding of RSLinx Classic. From what I can make out from the RA website and...
Replies
9
Views
2,355
Besides a $3,000 license to purchase a RsLinx Gateway License for every remote computer network that I work on. Is there another way to get to a...
Replies
4
Views
2,686
Hi, I'm running FTView v9 on a VM machine. Host win 10 64 bit, virtual win 7 pro. I've come to configure communication on this project (1st...
Replies
2
Views
2,162
Good day, Does anyone know if the device shortcuts can be backed up, if they are stored in a SQL-Database?
Replies
3
Views
2,015
Hi, I am trying to read data values from CAT generator via monico(redlion) module to be displayed on factory talk view studio via RSlinx...
Replies
8
Views
4,736
Back
Top Bottom