Slc 5/04 Communication Problems
Hey everyone,
I am trying to communicate with a Slc 5/04 plc using the 1747-cp3 cable, RS232-DF1 driver and a laptop. I tried using a serial to usb converter (3 of them), and using the driver but was unsuccessful in configuring the driver. I proceeded to use a docking station (connecting the 1747-CP3 cable directly to the docking station) without the converter and I am still unable to configure the driver. I'm unsure what I am doing wrong and would really like some help. Thank you all for your help! |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Oct 2007
Location: Nashville, Tennessee area
Posts: 3,545
|
the serial to usb converter software may assign a different serial port.
liik in your com settings to see which port is actually being used when the cable is plugged in and change the rslinx setting to match that port. i hope this helps, james |
![]() |
![]() |
#3 |
Lifetime Supporting Member
![]() ![]() Join Date: May 2017
Location: Michigan
Posts: 915
|
Do you have an offline program file indicating what the comm settings in the PLC are? While the default setting is for DF1, it is quite possible that it has been changed (eg to DH485, which would require additional hardware to connect).
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Sep 2022
Location: Minnesota
Posts: 12
|
I check and always change the com port in rslinx to what I see in Device Manager. I have done this multiple times and cannot seem to communicate with the plc
|
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Sep 2022
Location: Minnesota
Posts: 12
|
I do have an offline copy of the program. I will check that and see what it is assigned as
|
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 715
|
I don't have the cable specs handy, but you will need a null modem serial cable to connect to the serial port on the 5/04. In RSLinx Classic, make sure the RS232 driver is set to the right COM port (visible in the PC's Device Manager) and then autoconfigure with the PLC connected. If it fails, first thing to try is a null modem adapter. If you absolutely can't get it to work...try with another 5/04. That PLC's port may be bad.
|
![]() |
![]() |
#7 | |
Member
![]() ![]() Join Date: Sep 2022
Location: Minnesota
Posts: 12
|
Quote:
|
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Sep 2022
Location: Minnesota
Posts: 12
|
This is the channel configuration found in the offline version of the PLC.
|
![]() |
![]() |
#9 |
Lifetime Supporting Member + Moderator
|
Do you have a data hwy plus cable?
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus |
![]() |
![]() |
#10 | |
Lifetime Supporting Member
|
Quote:
You need to know the Slave ID number, baud rate, and error checking method and then you need a good RS232 to Serial adapter and some luck to get that driver to work. Get a screenshot of the Channel Config with the "Chan. 0 - System" tab selected. Here's a good thread on the topic where Ken Roach breaks down the details very well: http://www.plctalk.net/qanda/showthread.php?t=126718 Last edited by OkiePC; September 30th, 2022 at 12:39 PM. |
|
![]() |
![]() |
#11 |
Member
![]() ![]() Join Date: Sep 2022
Location: Minnesota
Posts: 12
|
|
![]() |
![]() |
#12 | |
Lifetime Supporting Member + Moderator
|
Quote:
Can you do this? there is a chance the DH+ cable is the only what for it to work The other way is.... reset the PLC to factory default and then download the program again after you change the system settings, but if there are any changes in the CPU that are NOT on the offline program they will be lost forever so its a risky way OR other way number 2) Do you have a spare CPU? If I were you I would get one (cheap on ebay) and download your offline program and install it to see if it works as expected. The other option is buy a DH+ cable, we sell an aftermarket one but its not cheap and the spare 5/04 would be your cheapest way.
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus |
|
![]() |
![]() |
#13 | |
Member
![]() ![]() Join Date: Sep 2022
Location: Minnesota
Posts: 12
|
Quote:
|
|
![]() |
![]() |
#14 |
Member
![]() ![]() Join Date: Sep 2022
Location: Minnesota
Posts: 12
|
Update!!!!
I was able to use the suggestion by OkiePC and use DF1 polling master. I changed every parameter that was set in the plc to match parameters in the Polling master. I was able to talk to the plc, make my changes and download to it. Thank you every one for the support. I really appreciate it. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
SLC 5/04 Communication Issue | jduong17 | LIVE PLC Questions And Answers | 16 | September 30th, 2022 08:23 AM |
PV c600 communication with SLC 5/04 | zeeshan123 | LIVE PLC Questions And Answers | 0 | August 13th, 2016 04:13 AM |
How to establish communication with the SLC 5/04? | rodrigoevaldo | LIVE PLC Questions And Answers | 2 | October 11th, 2011 12:50 AM |
slc 5/04 communication | randy | LIVE PLC Questions And Answers | 7 | December 20th, 2005 01:08 PM |
slc 5/04 div instruction problems | eastkodakguy | LIVE PLC Questions And Answers | 4 | August 11th, 2003 03:57 AM |