PLC with no mains supply

Goody

Member
Join Date
Apr 2002
Location
Huddersfield W Yorks UK
Posts
1,081
Today I was called to a customer with an electrical fault on a machine. I have specialized a little on this type of machine and I have also written a program to retro-fit these machines, so I was glad to go. (I smelled a plc sale)

When I opened the control cabinet, There was already a plc doing the biz in there. (ah well, never mind, just repair the fault) The PLC was an old Mitsubishi F1.

As I was tracing the wiring (not a drawing or nowt you know) I looked at this plc and there was no mains voltage to it.
There were inputs and outputs wired and the outputs had a common 240V supply.
The mains voltage terminals had options for 240V and 110V but there was no wires in those terminals at all.
The plc had no lights on as the problem was with the main power contactor not coming on.

I found the fault (mangled wire) and put the power on.
The plc sprang to life with inputs and outputs going on and off but still with no supply to the L1 N1 N2 terminals. :confused:

I then found that there was another 24VDC supply and this fed the plc's 24VDC service supply. (the one you use for inputs)

This must be able to supply the plc with what it needed through the back door, because it works fine and the age of the plc means it must have been working fine for years. Has anyone seen this before?

I scratched my head for a good while. I was sure either the plc was not used or someone had been messing..............
 
You may want to check the specs on that Goody, alot of the older models had the option of using ac or dc, when ac was used the dc side could be used as a power supply but you could use a dc power source to power them with no ac applied. I dont know mitsi but many other brands did this.
 

Similar Topics

Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
0
Views
18
I know this topic has been brought up a few times, but i had some specific questions. I have installed several 1783-NATR devices and they have...
Replies
0
Views
37
Hello We have installed several G.E. Fanuc 90 70 PLC Everything was ok but suddenly we can not communicate anymore with any PLC with the software...
Replies
0
Views
33
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
51
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
92
Back
Top Bottom