Hi Guys,

Need your expert advise.

Is it possible to connect ControlView HMI with ControlLogix over DH+. Any details or example would be of great help.



Background----

The plant is running with ControlView HMI and PLC5 system over DH+. A upgrade is suggested, but we have our concerns over CLX communication with ControlView over DH+



Thanks
 
rPraveenkum said:
Controlview is very old visualize software.
I don't think so it will work with clx

I was wondering, if it works with PLC5 over DH+, we might have chance of it working with CLX over DH+ using a DHRIO module.
Any suggesstion or example would be of great help.
 
It should work

The comms drivers in ControlView will only be capable of addressing PLC/SLC style addresses.
In the ControlLogix you will need to configure "SLC/PLC Mapping" which is simple enough.
 
If it were me, I'd upgrade the DOS-based ControlView and not the PLC-5 controller. But that's me.

Classic PLC-5 controllers used an addressing mode called "logical ASCII addressing". SLC-500 and PLC-5 Enhanced/Ethernet/ControlNet controllers use an addressing mode called "logical binary addressing".

I think the ControlLogix will respond to both types of addressing over the 1756-DHRIO module. I don't know which type of addressing ControlView used. Those two factors of uncertainty would make me want to measure, analyze and test before moving forward.

This should be fairly easy to test. Your test ControlLogix only has to have the PLC/SLC Mapping defined for all the data tables in the PLC-5. You wouldn't have to totally translate the application to ControlLogix just to test the HMI communications.
 
Ken Roach said:
Classic PLC-5 controllers used an addressing mode called "logical ASCII addressing". SLC-500 and PLC-5 Enhanced/Ethernet/ControlNet controllers use an addressing mode called "logical binary addressing".

I think the ControlLogix will respond to both types of addressing over the 1756-DHRIO module. I don't know which type of addressing ControlView used. Those two factors of uncertainty would make me want to measure, analyze and test before moving forward.
Aha!
I always wondered why the ControlView node setup had options for "PLC-5" and "Enhanced PLC-5"

Ken Roach said:
If it were me, I'd upgrade the DOS-based ControlView and not the PLC-5 controller.
This should probably be the priority.
From memory, I don't think ControlView will run on a Pentium processor.
Actually, it's probably the underlying Chronos operating system that has the problem.
Migration to RSView 32 is fairly easy and the "look & feel" will be very familiar.
 
Ken Roach said:
If it were me, I'd upgrade the DOS-based ControlView and not the PLC-5 controller. But that's me.

I understand upgrading ControlView is the best option, but this will have to wait for another year. For now we are limited to partial migration..... "management call".
 
Thanks guys for all the help.
Do you have any example document that can help me convince the customer that this phased migration will work

 
The 1756-DHRIO module has a "default slot" setting so that when DH+ messages arrive at the module that do not have a Remote Link ID embedded in them, the -DHRIO routes them automatically to the ControlLogix controller in the default slot.

The default slot is zero, but the 1756-DHRIO can be configured using RSLinx to set the default slot to a different slot.

I can't tell you if the DH+ addressing used by ControlView is also supported by the 1756-DHRIO. ControlView probably won't be supported by RA for this application, since it has been obsolete for 4 generations of Microsoft/Intel platforms and 2 generations of Rockwell platforms.

But you can test it for yourself by hooking up a ControlLogix and 1756-DHRIO to the ControlView system. That's the only way you can be sure.
 

Similar Topics

Hello! I am currently working on a migration and I need to migrate a ControlView application to FactoryTalk View, reviewing some manuals I have...
Replies
5
Views
1,815
I am traying to convert an aplication from ControlView to Rsview, but I need to run the aplication. I have installed MSDOS (ver 6.22) but when I...
Replies
2
Views
4,223
I have no experience with Eaton HMIs. I downloaded the Galileo software and I am trying to get the file on a HMI (XV-102-H3-70twrl-10) to modify a...
Replies
4
Views
40
Sorry for my lack of knowledge, beginner here. Yesterday, we had a Pro-Face SP5000 HMI fail on us. The technician said that the HMI had the blue...
Replies
0
Views
36
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
53
Back
Top Bottom