Here is the manual, there is a lot to take in if you want to understand how it works, look at section 3 it gives the list & explanations of the buffer memories, there are many parameters that could be used like type of PT100, ranges, filters, offset & span settings the list is endless, on your other post regarding the subtraction of a value as an offset this could have been done within the program for calibration purposes but it's a lot of work so most people do not bother just add or subtract a bit around the expected range. Using the configurator is far easier.
I have just had a quick look at those addresses 164 & 165 and these seem to be offset settings but again chinenglish manuals do not make it very clear so are not the mode as such, I have only used the FX PT modules on all Q series I used 4-20ma and head converters in the PT100 probes, this gave us a quick way to calibrate them without touching the PLC code or pages of settings on HMI's.
https://dl.mitsubishielectric.com/dl/fa/document/manual/plc/sh080142/sh080142o.pdf