I'm sorry if this has already been talked about. When I did a search I only found information about CP's.

Anyways, I have a 7 315 2PN/DP's. Each of these processors has 2 ports on the front of it for profinet.

From what I gather from the manual and siemens site, each processor has 3 mac addresses. The mac address of the device(mac) the mac address for port 1(mac +1) and the mac address for port 2(mac+2).

Now the mac addresses printed on the face of each processor is different. Also from the command prompt if I ping any of the processors and the do an "arp -a" I get a unique mac address for each device.

The problem, when all of the processors are connected to a managed cisco switch it freaks out for having a duplicate mac addresses on differnet ports(Flapping), and also for having multiple macs a a single port.

After talking with IT and doing reading it looks like it is do to LLDP (Link Layer Discovery Protocol), which I see on older CP's it was an option that could be disabled.

The closest thing I see on the processor is an option that can be enabled on either port for "End of topology discorver"

Has anyone seen this before?
 
Just giving this thread a bump to see if I can catch anyone's attention this time around.
 
..

The problem, when all of the processors are connected to a managed cisco switch it freaks out for having a duplicate mac addresses on differnet ports(Flapping), and also for having multiple macs a a single port.
...

In what way they are networked? Remember those ports are switched ports, its two ports out + one port to cpu. So it does have multiple macs in one port. Duplicate mac's there would be if also cpus are connected together.
 
Last edited:
In what way they are networked? Remember those ports are switched ports, its two ports out + one port to cpu. So it does have multiple macs in one port. Duplicate mac's there would be if also cpus are connected together.

I'm not sure what you mean.
I know that each PLC has a unique MAC address, and Port 1 is the MAC address +1 and Port 2 is the MAC address +2.
Each PLC has a Ethernet cable running from Port 1 to our Cisco switch.

JesperMP said:
Any difference if you enable the "End of topology discover" ?
I have not tried it yet since I am not on site yet, I was curious if anyone has had to do this before.
 
I'm not sure what you mean.
I know that each PLC has a unique MAC address, and Port 1 is the MAC address +1 and Port 2 is the MAC address +2.
Each PLC has a Ethernet cable running from Port 1 to our Cisco switch.

This is only cpu:

Code:
PORT1--SWITCH--PORT2
          |
         PLC

So there is multiple macs behind one port of Cisco switch.

Is this how you network is connected:

Code:
PLC1_SWITCH_PORT1---CISCO---PLC2_SWITCH_PORT1

There must not be any other link from PLC1 to PLC2 than trough CISCO, otherwise it will find same PLC trough both ports.
 
Layout of Cisco Switch.

---------
|Cisco |
|Switch |
| |
|Port 1 |-----PLC 1 port 1
|Port 2 |-----PLC 2 port 1
|Port 3 |-----PLC 3 port 1
|Port 4 |-----PLC 4 port 1
|Port 5 |-----PLC 5 port 1
|Port 6 |-----PLC 6 port 1
|Port 7 |-----PLC 7 port 1
|Port 8 |-----HMI 1
|Port 9 |-----HMI 2
|Port 10|-----HMI 3
|Port 11|-----HMI 4
---------
 
Layout of Cisco Switch.

---------
|Cisco |
|Switch |
| |
|Port 1 |-----PLC 1 port 1
|Port 2 |-----PLC 2 port 1
|Port 3 |-----PLC 3 port 1
|Port 4 |-----PLC 4 port 1
|Port 5 |-----PLC 5 port 1
|Port 6 |-----PLC 6 port 1
|Port 7 |-----PLC 7 port 1
|Port 8 |-----HMI 1
|Port 9 |-----HMI 2
|Port 10|-----HMI 3
|Port 11|-----HMI 4
---------

If there really is nothing else (no cables in port2's of plc's), then duplicate mac's alert seems very odd.
 

Similar Topics

What is the simples way to do a double click of a button in a ladder logic. New here and I hope this has not been asked before.
Replies
22
Views
527
Hi All, I'm keep getting double quotes in between selections rather than the beginning and the end. Here's the script and please help to find...
Replies
7
Views
796
Hi! I am using a TM200CE40T PLC from Schneider to write data over Modbus. I have used Memory words (%MW) before using the Write variable...
Replies
1
Views
527
Hello All, IÂ’m starting a new project where the plc is connected throught LAN with external software which write some data on PLC db, obviously...
Replies
1
Views
503
Hello. I have been working on my first plc project for a while now. I just ordered all the parts that I need and before I did that, I created the...
Replies
10
Views
2,018
Back
Top Bottom