Siemens ET200b issue

dwoodlock

Lifetime Supporting Member
Join Date
Nov 2012
Location
Cincy Area
Posts
574
I was curious if anyone has ever in their experience come across and issue similar to mine with the same hardware.

Basically this remote i/o block was repeatedly blowing 2.5A main fuses. after the (some large#) occurance of the fuse immediately blowing I got called in.

I supplied power to the module with a desktop 24vdc power supply, where I could set the current limit below the fuse so that I could try to troubleshoot the issue, and find out where the short was stemmed.

The module has 8-O/24-I and I have basically found that with power supplied to the Input side, the module works fine. As soon as you supply power to the Output section, current maxes out, and control voltage drops out. This even occurs when I disconnect all output wires from the module.

At this point Im basically thinking that its an eletronics issue, or something has died becuase of the reoccuring current spikes, perhaps someone here can point me in the right direction?

I know there are people on this board who've forgotten more than I've learned.

-Thanks in advance

Dan
 
so if you get your meter and check (wires disconnected) from output to common- what do you see?
shorted?
ie.. pin1 to pin 65

200s1.jpg
 
thanks

sometimes someone pointing you in the obvious direction is a huge help! you the man
 
Last edited:

Similar Topics

I have a Siemens analog output module 0 to 10V(6ES7135-0HF01-0XB0) which is connected to a analog meter 0 to 10v. this meter sometimes shows...
Replies
9
Views
2,649
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
2
Views
91
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
9
Views
284
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
103
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
159
Back
Top Bottom