Good day folks,
We have an L71 processor (v30.02) in a rack with an EN2T connected to the plant network & another (v10.007) used for IO only - both are connected to a managed switch.
The other day, we had a brief power/network outage. When everything came back up, the IO network EN2T had a "minor" IP address conflict fault. Looking at the module properties in Studio 5000, The general tab showed the correct Ethernet Address (grayed out) while on the Internet Protocol tab, the Physical Module IP Address, Subnet Mask & Gateway Address fields were now all 0.0.0.0. I was able to re-enter the correct information and restore comms but the fact that communication to all remote IO racks was lost for a while really caused our plant some grief. So here are my questions:
1. Any idea why this happened?
2. What can be done to prevent this from happening again?
Thanks in advance.
We have an L71 processor (v30.02) in a rack with an EN2T connected to the plant network & another (v10.007) used for IO only - both are connected to a managed switch.
The other day, we had a brief power/network outage. When everything came back up, the IO network EN2T had a "minor" IP address conflict fault. Looking at the module properties in Studio 5000, The general tab showed the correct Ethernet Address (grayed out) while on the Internet Protocol tab, the Physical Module IP Address, Subnet Mask & Gateway Address fields were now all 0.0.0.0. I was able to re-enter the correct information and restore comms but the fact that communication to all remote IO racks was lost for a while really caused our plant some grief. So here are my questions: