The new button has been added and logic is all set for it. It is conveyor on/ off button and working properly but I was not able to make it display an alarm when it is switched off. How you make an alarm display on hmi ? Is it using a Factory talk view or RSlogix 5000 software? Thank you, Ziya
You need to use FTView Studio ME (Machine Edition), and go into the left tree of your project.
Do you have RSLinx Enterprise Configured to point a Short Cut to the PLC?
If not, you should do that first.
To configure a short cut, you need to look as some YouTube Videos if you do not know how to do this.
This also explains the process...
http://bryceautomation.com/index.php/2017/09/13/factorytalk-view-project/
Getting back to Alarm Configuration
Open the Folder "Alarms"
Double Click "Alarm Setup"
Click "Add Trigger"
If you are going direct to the PLC (which I recommend), you can browse to the tag (If you have offline project defined, or you are online with Processor), or you can just type it in in the following format.
{[PLC]PUMP_STOPPED}
After you have your trigger defined, now you have to assign the trigger to your alarm message, on the second tab "Messages".
You will need to add an object to your project to display the alarm "Alarm List" Object.
There is a bit of configuration (check boxes and pull-downs) but it is self explanatory.