Momentum - Schneider - How does one configure the IEC totalizer block?

jhakh

Guest
J
Using an analog input, what does one put into the totalizer block to make it count based on the 4..20ma at channel 1
need a BOOLEAN output when the total gets to 100Liters and a place to put in the reset instruction.
Tks
 
The Totalizer function block is used to integrate an analog value over a specific time interval. An boolean output is generated after the total exceeds a preset.

Some of the input pins are:
MODE: selects the operating mode, needs to be formatted as a "Mode_TOTALIZER" this input is actually two "Bool" values rst=>resets totalizer and hold=>pauses the operation
TR_S: this is the initiating signal, it is a "Bool"

The priority of these signals is:
TR_S is above all other inputs.
rst is only above over halt.
 

Similar Topics

Trying to identify the Modbus RTU registers that are in use in the Function block programming in the PLC program. I have a Kohler DEC 550...
Replies
0
Views
140
Dear Friends, This time I have been assigned a project, where machine has Schneider Momentum 171CCC78010, 171CCS7600 installed. I don't have...
Replies
8
Views
2,692
Hi..I am working on a project involving Momentum PLC 171CCC98030. I am doing its programming in Concept 2.6 SR7 (Demo Version) . I have following...
Replies
2
Views
1,807
Environment cpu 171 CBU 98090 170 AAI 140 00 170 ADI 350 00 170 ADO 350 00 Unity Pro V8.0 I use RSLogix 500 & 5000 all the time, have also used...
Replies
2
Views
4,322
I have a customer that would like to move away from Wonderware to RSlogix5000. They currently have Schneider TSX PLCs at their location and would...
Replies
3
Views
2,473
Back
Top Bottom