Good Evening ,
I would like to test some message instructions , and other modifications
in a SLC 500 5/05 Processor in the office without 2 racks of I/0 . Is it possible to load a program in a 5/05 processor without I/O and test without faulting out the processor ?
Thanks so much for your help .
Disable I/O in Status File
Go to the Processor Status file in the project tree. Then click on the IO tab. Put ZEROS in all the slots that represent the number of slots in your combined chassis to disable them and prevent the Processor from requiring them to be present. That should do it.
Another thing you can do is have the IO Config empty of all cards, create a binary file B10: that is as many words long as slots in the rack.
Then in your program B10:1/0 to 1/15 can be your "inputs" and B10:2/0 tp 2/15 can be your "outputs". This would be easier to test by simply toggling the bit when online to simulate an input going on or off.
If you need analog in/outs create an N11: file.
I've experienced a strange issue with 5/05s where the processor will fault when there is no I/O, even if none is configured in the project. If you have an existing rack with I/O, the workaround is to just MOV zeroes to the outputs on an otherwise blank ladder. Then nothing can happen.
Hello all, I have an SLC 5/05 series C (pic attached) but when I try to download a program it say it is a different series with a different FRN...
3,848
Good Afternoon, I plan on replacing some SLC 500 PLC's with CompactLogix. Could you tell me what the equivalent processor is in the...
2,273
Good Morning , I cannot believe I forgot how to do this. It seems like I have been spoiled with everything being Ethernet. I have a SLC 500...
2,747
Hello. I am learning Allen-Bradley PLC programming using the RSLogix 500 emulator. So I need some help pls. I am using the RSLogix Microstarter...
4,249
Hello All, I am having an issue with configuring the processor for a SLC 500/03. Every time I download it switches the processor to a different...
2,333