WinCC + Clients-What is required from Siemens

Greg Fowlds

Member
Join Date
Apr 2004
Location
Currently, Waiheke Island, NZ
Posts
123
Have a project that customer requires WinCC V7.0 (Not Flex)
1 x Server.
3 x Clients.
Less than 2000 tags to/from PLC, Less than 512 Tags for trends.

Am getting lost with what to order, have never used WinCC before or even seen it running anywhere.

A RC2048 (6AV6381-2BP07-0AX0) has Run Time + Configuration.
Is this classed as a server?
Would this run as an operator station as well or only as server?

A RT128 (6AV6381-2CA07-0AX0) as a client.
Will the RC2048 configuration handle the client as well as server or do I have to purchase a configuration for Client and a different one for server.

Running Siemens online order system there is no heading for server only.

Edit: Found some more information on Siemens site.
Does this sound correct
1x WinCC/Server
1x RC2048
3x RT128
 
Last edited:
Yes you are right.

For the server: You need WINCC RC 2048 tags on the server + wincc server add on
For each client: You only need the basic WINCC RT128 for each client

512 Archive tags for trends is included in the basic license for RT / RC.
 
Just take a look at the compatibility list so you know what you need from the PC side.

As you can see, the server station can't run in Windows 7 SP1 for example.
 
Last edited:
Yes you are right.

For the server: You need WINCC RC 2048 tags on the server + wincc server add on
For each client: You only need the basic WINCC RT128 for each client

512 Archive tags for trends is included in the basic license for RT / RC.
Dear rohan tandon
For each client: You only need the basic WINCC RT128 for each client

If we exceed the number of 128 Tags then what will happen in RT Client PC..??

Thanks.
 

Similar Topics

I am working on a project where I need to create a visualization screen (HMI Panel or PC) using wincc tia portal v16. It will be connected to the...
Replies
3
Views
531
Hi, Is it possible to connect WinCC 7.0 Clients to Wincc 6.2 Server?
Replies
0
Views
2,500
I am doing a test with wincc v6 I configure a wincc server and try to have some client you know when create a wincc project it will be generated...
Replies
1
Views
4,450
Does anyone happen to know how to install the graphic picture in HMI when I go into blower selection there are no graphics shown not only blower...
Replies
1
Views
63
Hi folks, I'm not as accustom with Siemens & WinCC, however I've been asked to increase the amount of data an existing application is logging...
Replies
2
Views
65
Back
Top Bottom