GE 90/30 Sweep Time

biil2769

Member
Join Date
Dec 2004
Location
wisconsin
Posts
7
Is there a way to see the scan time, like a special utility register, in the logic itself to be displayed by a touch screen/operator interface?
I know it shows scan time in LM90 and Versa pro when connected to PLC.
We just want to monitor the scan time.

Bill
 
GE Fanuc chose not to make that information available directly in the ladder program.

You can write logic to execute Service Request #16 every scan. That will return a cumulative time in 100 microsecond increments. The difference between two successive scans is the scan time for the last scan.
 