Modbus RTU communications connection

BobB

Lifetime Supporting Member
Join Date
Jun 2002
Location
Sydney
Posts
4,551
Just working on a job with a heap of Schneider power monitors connected to my PLC with Modbus RTU.


There are the usual D0 and D1 connections plus 0 volt that is being used these days as a 3 wire connection and 0 volt ties all the units together at the one voltage ;level - that is all good.


The Schneider documentation also shows the drain wire of the cable connected to a terminal with an indication of a circle with 2 horizontal lines through it. Have never seen that symbol before.


Would anyone know what it represents at all please? If it is just a loop through connection for the brain wire that is good.


I cannot see it being anything else as there is no earth connection on the meters but who knows.
 
Last edited:
Thank you muchly - one of the links clearly shows the shield looping through and then grounded. I thought it was a loop through as the meter has no ground connection.
 

Similar Topics

Hi All, I have a question would like to ask the experts: my system has two Rx7i PLCs and I'm having them communicate with an RTU (D25) via modbus...
Replies
2
Views
2,046
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
40
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
6
Views
133
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
212
Hi, I'm having an issue with a mircologix not transmitting out. The current setup is a mircologix 1400 connected to a Guardian 100 Radio...
Replies
1
Views
108
Back
Top Bottom