Rslogix500 input issue

gouldmx01

Member
Join Date
Sep 2018
Location
sct
Posts
11
Hey guys, first time poster here and very new to the PLC world, i'll cut to the point:

I am using the rslogix 500 program and i have a photo-eye attached to an XIC bit in my program. I've been having issues with the process recently so i looked to the program and found that the bit that the eye is attached to seems to be flickering very subtlety, before i go trying to change out some photo-eyes my question is ; is this very faint flickering enough to disable my output? it goes on and out multiple times within milliseconds!:confused:
 
Welcome to the PLCTalk forum !

When you say that the "bit" is flickering, do you mean the indicator on the Input module?

You're either seeing rapid switching of the input state, or a low voltage that is hovering around the 1 vs. 0 threshold.

Either way, start by checking for loose wires (both power and common and signal).

A "flickering" input can definitely cause your logic to not work the way you expect.
 
+1 For Ken's suggestion. In my experience the problem is almost always the field device or the cable going to it. If this process has been running for more than 6 month, and no changes have been made to the program recently, there is a 99.99% chance that the problem is a bad eye or bad cable. You mentioned flickering, so I'm going to guess bad cable.

Bubba.

PS...
Welcome to the forum!
 

Similar Topics

So here's my situation, I have been tasked with modifying the logic to mimic a button press in the PLC. I have two identical machines however one...
Replies
6
Views
538
Hi, I'm using a Micrologix1500 and it doesnt have the SCP (Scale with parameters) block. I have a 1769-IF8 analog module and need read the inputs...
Replies
10
Views
3,751
when using a micrologix and programing a 4-20ma input does 4ma input = a value of 0 and 20ma = 32767 or is 4ma = 20% of 32767.
Replies
5
Views
1,973
I am new in PLC Programming. We have AB SLC 5/03 and RSLogix500 program. We have a new analog equipment that would be connected to Input Analog...
Replies
2
Views
4,941
Hello, I'm new to programming. I'm using RSLogix500 to modify an existing program for a SLC500. My plan was to use one of the existing inputs...
Replies
26
Views
1,983
Back
Top Bottom