FEN20_16DXP Studio 5000 Logix designer V32.02.00 (CPR 9 SR 11)

dahnuguy

Member
Join Date
Mar 2007
Location
SC
Posts
720
Can ping module and shows up in Hardware config with no faults and shows "running" in status.
Can read inputs from the FEN20_16DXP.
LEDs on module respond in relation to the inputs that are on.

When I write to the outputs nothing changes.

Wired like this:
https://www.turck.us/attachment/G1038.pdf page 6

FEN20_16DXP:C.Data[16] = FF Activate output
FEN20_16DXP:C.Data[17] = FF Activate output

FEN20_16DXP:I.Data[1] Input value changes with inputs.

FEN20_16DXP:O.Data[1] "7" Output value
Values are in the output register changes but the actual hardware output does not come on.

Any ideas?
 
Do they have an updated user manual that describes Bytes 16 and 17, the "FF Activate Output" in detail ? What I read shows only bytes 0-15, and the only functional bit in the Configuration assembly is for Quick Connect.

Are the Input and Output assemblies 16-bit INTs ? Is the Config assembly made up of INTs or SINTs ?
 

Similar Topics

Can this module be controlled by a Micrologix 1400 and if so how is the addressing or Messaging done. I am reading the Turk manuals and all they...
Replies
4
Views
1,215
Hi I wanted to check if anyone is using the Turck FEN20-EN1 as a NAT it looks like you can actually do up to 5 1 to 1 NAT. I have 10 panels...
Replies
7
Views
1,676
Hi all, Hoping someone out there has used these units and can give some honest feedback, are they great or rubbish? From what i can tell, they...
Replies
0
Views
1,230
Hey all, I'm trying to set 4 of the last I/O to be outputs. The manual says to push the set button (which I assume is the one next to the rotary...
Replies
4
Views
3,245
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
4
Views
35