How to Number Terminal Blocks

Tim Ganz

Member
Join Date
Dec 2010
Location
Dallas, Texas
Posts
685
I have seen terminal blocks labeled 1-200 or similar and I have seen them labeled with the same number as the wire in the terminal. What is the correct way? And why 2 different methods?
 
Tim,

i have seen the terminals labled corresponding to the wire number - easier to deal with. there can be nultiple terminals with the same number, a jumper wire or shotring bar is used to connect the terminals.

i have also seen the terminals labled X-xxx where X is the terminal block number/letter and xxx is the terminal itself.
this mostly comes fro large OEM's who mass produce.

i always try to use the wire number approach. its easier on maintenance.

regards,
james
 
Correct is whatever works for you: Does your customer/ company require it a certain way? If so, you are tied to their requirements.

I'm not constrained by any convention, I have always used #TX-??? where # is the enclosure number, X is the terminal blockset in the enclosure (if there are more than one set of terminal blocks) and ??? are terminals 1 - however many are needed plus a few for expansion if that is a possibility for a given project. YMMV, the main thing in my mind is to be consistent as you can be so that those that follow after you do not have to learn a new system for each new project. This convention helps when reading a schematic that has wires going to numerous locations.
 
To me, the terminal number should be the wire number. Anything else seems to only add confusion. Keep it simple where you can, there are plenty of non-simple things we must deal with.
 
We have one machine where there are about 70 terminals labeled 209 and 209 is the +24 DC that goes to all field sensors and then from each sensor to the plc that wire is labeled with the PLC input #.

When we have a crushed conduit or similar and the fuse for 209 clears we can find the short but then we don't know what device that specific 209 wire is feeding so we have to remove Panduit covers and start tugging the wire to see where it goes.

Seems like the numbering 1-70 for example we could look at the print and see the field device fed from 209 on that terminal.

It seems because of this the sequential numbering being different from the wire number may be better or am I missing something?
 
To me, the terminal number should be the wire number. Anything else seems to only add confusion. Keep it simple where you can, there are plenty of non-simple things we must deal with.

Several years ago it was easier to put the wire number on the terminal number and then everything matched. Since the smaller IEC terminals have become so popular it is more difficult to do the same.

I now just show wire # xxxxxxxxx landing on terminal TB5-7 (terminal 7 of terminal strip 5, don't ask me why it's TB instead of TS, just tradition I guess).

If we are using multi-level terminals then then TB5-7's top level terminal may just be a square box, TB5-7's middle level terminal is a square box with a diagonal line thru it.

May not be perfect but it works for most situations.
 
As MikeW said above, whatever works for you. I can see where you may not be able to fit a long number on the new smaller TB's, even if you have a TB marker printer. Large systems can have some long numbers.
 
Correct is whatever works for you: Does your customer/ company require it a certain way? If so, you are tied to their requirements.

I'm not constrained by any convention, I have always used #TX-??? where # is the enclosure number, X is the terminal blockset in the enclosure (if there are more than one set of terminal blocks) and ??? are terminals 1 - however many are needed plus a few for expansion if that is a possibility for a given project. YMMV, the main thing in my mind is to be consistent as you can be so that those that follow after you do not have to learn a new system for each new project. This convention helps when reading a schematic that has wires going to numerous locations.
Mike, I have seen designers who append the "source cabinet" number to every wire number that leaves the panel. So, wire number 9480+971 would be originating in panel number 971. It makes it easy to find the power in a multi-panel job, where there are interlocks, and such.
The OP's problem is not a terminal block problem...it is a design problem. The designer should have added some supplementary protection when fanning out power to many places like that, IMHO. :eek:
 
As others have said - what your customer wants.
Personally I now use The Terminal block system . 2 advantages not so far mentioned -
1 The cores of multi-core cables align with the terminal numbers
2 With electrical CAD drawings an easily generated cross reference to the terminal block gives not only the wire , but the destination as well and ties to the cable reference.
Paul
 
I utilize the Tx-y system. Where x is the terminal strip and y is the location on the strip. For multi circuit blocks I append the end with a letter to represent what circuit the wire should land on. I went to this system because we use pre-printed labels. The quantity and variety of labels I needed was getting a little out of hand. Now I can use 0-100 and a-d to label and entire panel.

I also prefer to have my wire numbers reference the line number on the drawings instead of the termination point.
 
Mike, I have seen designers who append the "source cabinet" number to every wire number that leaves the panel. So, wire number 9480+971 would be originating in panel number 971. It makes it easy to find the power in a multi-panel job, where there are interlocks, and such.
The OP's problem is not a terminal block problem...it is a design problem. The designer should have added some supplementary protection when fanning out power to many places like that, IMHO. :eek:

No kidding. Unfortunately it is far too common on machines that I see. I have one that right now is periodically doing something similar except it's not a dead short, just enough to drop the 24V to the entire machine for a split second (which in turn drops out the drives). I've been up and down that machine with a fine tooth comb looking for something but haven't found it yet, very maddening.

As far as an opinion for the OP I like labeling the terminals with the wire number if that is practical. And for the love of all that is holy do not skimp out and not label the wires just because you have a drawing showing what number terminal they should be on in the block.
 

Similar Topics

I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
Replies
3
Views
118
Complete noob here, using a Click C0-02DD1-D to run a test stand. Requirement is to turn on motor run for X seconds, turn off and dwell for X...
Replies
6
Views
1,067
Hi, I have this weird issue whenever I try to change the SNN from a Point IO Im missing the three ... dots to open the pop up and change it...
Replies
4
Views
609
I'm doing my first PanelView 5000 application with Logix View Designer v8, and am of course jumping in headfirst. One thing I don't find is a way...
Replies
4
Views
690
Hi PLCs.net! I was curious: How many axis can a B&R APC910 control? Is there a hard limit like certain AB controllers? I'm new to B&R, so would...
Replies
0
Views
365
Back
Top Bottom