Hello

I have a panelview 1000 that I am looking to migrate to PanelView 7 Perf. I have this connected to two devices (One PLC (SLC) and One DCS(DeltaV VIM Inteface)) thru ethernet IP. I purchased the New Model and also did a upgrade on the interface (VIM2) module with a ODVA EThernet IP Driver. Panel View 7 says is ODVA Ethernet IP complaint. Problem is that the old Class 1 COnnection on the panelview is not longer possible with the newer versions thru FT View since they use RSLinx Enterprise, and I cannot find a way to create a generic enbt or a Class/Service connection. Someone has experience integrating PV7 Perf with other platforms thru Ethernet IP. Iknow about the generic data OPC server on FT View but I need this communication to be Eth/IP.

Please advise.
 
This is definitely a challenge.

Please clarify; does the DeltaV VIM module act as the "scanner" with the PanelView as an "adapter", or the other way around ?

If the DeltaV VIM module is an "Adapter", then you should be able to use the RSLinx Enterprise Direct Connectivity technique to read and write Parameter Objects or Assembly Objects.

https://rockwellautomation.custhelp.com/app/answers/detail/a_id/547266

But if the PanelView Plus needs to be the "adapter" or "slave" device for a cyclic I/O connection, that's a feature that the PV Standard had but the Plus does not.

I understand that the PanelView 5000 product re-introduced that feature, but I have not worked with that and do not know if it could be used with a third party device.
 

Similar Topics

Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
127
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
64
saludos a toda la comunidad Hace unos días he venido presentando pérdida de comunicación en una terminal hmi, anexo las imagenes de la secencia...
Replies
1
Views
92
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
80
Can anyone help out with this Panelview Plus Performance Email. I keep getting an "unable to activate connection "smtp-mail.outlook.com". I've...
Replies
4
Views
202
Back
Top Bottom