rankhornjp Member R Join Date Dec 2008 Location Georgia Posts 241 May 23, 2017 #1 I have a WW application where a "light" is turned on by a tagname who's address is I:56/03. The problem is that I don't have a slot 56 in my plc. Any idea what this address is? Thanks
I have a WW application where a "light" is turned on by a tagname who's address is I:56/03. The problem is that I don't have a slot 56 in my plc. Any idea what this address is? Thanks
mort81 Member M Join Date May 2014 Location Indiana Posts 88 May 23, 2017 #2 PLC 5 and SLC 500 use Rack - Group - Slot addressing. I'm assuming by what you stated your Input is really I:056/03, which would be rack 0 group 5 slot 6 input 3.
PLC 5 and SLC 500 use Rack - Group - Slot addressing. I'm assuming by what you stated your Input is really I:056/03, which would be rack 0 group 5 slot 6 input 3.
rankhornjp Member OP R Join Date Dec 2008 Location Georgia Posts 241 May 23, 2017 #3 Ok, so what address would I look up in the plc?
rankhornjp Member OP R Join Date Dec 2008 Location Georgia Posts 241 May 23, 2017 #4 The input source looks like this
proof Member P Join Date Jan 2014 Location Illinois Posts 161 May 24, 2017 #5 Look up I:056/3 in the PLC.