Wonderware to RSLogix500 address question

rankhornjp

Member
Join Date
Dec 2008
Location
Georgia
Posts
241
I have a WW application where a "light" is turned on by a tagname who's address is I:56/03. The problem is that I don't have a slot 56 in my plc. Any idea what this address is?

Thanks
 
PLC 5 and SLC 500 use Rack - Group - Slot addressing.

I'm assuming by what you stated your Input is really I:056/03, which would be rack 0 group 5 slot 6 input 3.
 