1769-HSC Counts Not Working

selectionplc

Member
Join Date
Jan 2017
Location
Over there
Posts
9
I have a 1769-HSC card connected to a CompactLogix and using RSLogix 5000. I have device simulating a pulse to the card. InputStateA0 is showing up as 0 then 1, then 0. The problem is that no current counts or stored counts show up.

This is my first time configuring one of these HSC cards. I've attached screenshots of my config. I've tried changing a bunch of configuration settings, but am not getting any different results.

I appreciate any suggests. Thanks.

HSC_Config1.PNG HSC_Config2.PNG HSC_Config3.PNG
 
Haven't used these modules but check tag

Local:"YOUR CARD SLOT":O.Ctr0En it should be set to 1 I believe

might be bit 0 in your control word on image config3.png

seems odd that the enable is in the output array but from what I read that's how she goes
 
Last edited:
Local:"YOUR CARD SLOT":O.Ctr0En it should be set to 1 I believe

Exactly. The use of the output lets your program start and stop counting as needed.

Secondly - if, during runtime within the program, something in the configuration area must be changed then you must follow this order.

1. Stop counting (CtrxEn = 0)
2. Change the configuration area value
3. Issue a 'Module Reconfig' message
4. Wait for the message to complete without error
5. Resume counting (CtrxEn = 1)
 
Hello All, I am just trying to learn up on these modules, as I installed my first last week. The intent is to use this module for 3 pulse flow meters. Hopefully, I have selected the right card for the job and have it wired correctly.. I have a couple questions and wasn't sure if I should start a new thread or post the questions here.. Let me know before I post the questions. I was unsure as far as how to wire and setup for reading flow in GPM

Thanks in advance
 

Similar Topics

Hello all. I am having trouble setting up my HSC to count pulses from a prox switch. I have it wired to the prox and I see the .InputStateA0...
Replies
3
Views
1,366
Here is my hail Mary pass I have a wheel that produces 33 pulses per revolution. The RPM of that wheel will be anywhere from 25.21 to 62.7 Pulses...
Replies
14
Views
4,694
Hello all. I have an issue that keeps plaguing me. The system has a 1769-L24ER processor and a 1769 HSC card. I am using CH.0 for tracking...
Replies
0
Views
1,463
Hello, Im trying to use a 1769 HSC card to get the RPM of a single channel encoder at 60ppr. Ive read the other threads of people have similar...
Replies
0
Views
1,691
Flashing Red OK Status indicator : Rockwell Automation Publication 1769-UM006E-EN-P - July 2013 Table 23 - Configuration Error Codes pg 117...
Replies
3
Views
2,173
Back
Top Bottom