Hi, does anybody know, what means error message on simatic OP7: "$551 AS address 2 not possible"?
I've got this message after downloading a programm into a new OP7.
Did I do something wrong? Is it possible to fix the operational panel? Thank You.
 
just try this

this message pop-ups only if plc port address & 1 defined in op7 configuration mismatches.

For that do this in protool. Match Communication peer address Parameter of PLC(controller) selected with actual PLC port address.
I hope this will solve the problem

OK Bye
Anmol
 
Hi, thank You for the answer!
I found configuration for peer parameter in Protool project:Address 2, Expansion slot 2, Rack 0. If I change them, how can I download new parameters to OP7? I've got allways the error message on the OP7 screen. Which port should I use IF 1A or IF 1B? I used port IF 1A for last download from my laptop. Is it possible to see OP7 own configuration?
Yours, Wal
 

Similar Topics

Hi, I'm new to Siemens Simatic OP7 HMI. I have an existing Siemens Simatic OP7 HMI, I want to store data of HMI in a database or excel file. Is...
Replies
3
Views
3,584
Good Evening , It has been several years since I used Siemens Software . I’m looking to purchase the software for a Siemens Simatic S7...
Replies
4
Views
447
I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
Replies
5
Views
526
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
Replies
2
Views
1,040
Hi. I have 2 files where I would like to see the ladder logic differences (similar to the Rockwell compare function). I am using TISoft Siemens...
Replies
1
Views
1,228
Back
Top Bottom