JagXtreme EDS Files

Join Date
Jan 2016
Location
UK
Posts
85
I have a production line where we have several scales on Controlnet back to a L55 Controllogix. All of them were JagXtremems. One of them went bad and we replaced it with a IND570. I can find pretty good documentation for IND570 and setup and ran the scale on ControlNet to a test processor on the test bench.
I am having trouble with the JagExtreme. When I go online to the controller on the production line and browse over Controlnet using RSNetworx, it just gives a bunch of 'question marks' for Jags because I do not have EDS file and I just can't find them anywhere on the internet.
Would there be issues if I scheduled the controlnet network with no EDS file for the Jags and added the new IND570 node for which I did download and install EDS file? I don't want to screw up the current system.
 
Would there be issues if I scheduled the controlnet network with no EDS file for the Jags and added the new IND570 node for which I did download and install EDS file? I don't want to screw up the current system.

I have never tried this.

That said, I have added to a controlnet schedule while missing some EDS files for the existing devices. I added the new devices, then used the Merge option, which appears to add scheduled data to the end of the existing schedule.

If you have some extra hardware - and if you don't you should likely get some - I would go online, upload the controlnet, save to a file, load it into your spare hardware, and experiment there. Verify that you can talk to one of the Jags (perhaps on a down day) and add your IND570, merge the changes, verify that it still talks to the Jag, etc

If you can't swing the hardware cost - and who can - your local Rockwell supplier should be able to lend you a demo case for a week that has a controllogix (likely newer than the L55), a controlnet card, and some coax jumpers that have proper terminations. They will not likely have a lot of demand for that sort of demo case any more.
 

Similar Topics

My PLC is an AB ControlLogix L62. I am communicating to a Mettler Toledo JagXtreme over Ethernet/IP. There is not an add-on profile in RSLogix...
Replies
2
Views
2,796
By way of background, I've written an Ethernet/IP driver for one of our products and we're ultimately going to attempt to get it certified by...
Replies
6
Views
178
Hello Friends We have 10 Powerfocus 4000 with DeviceNet, We need to backup the configuration, the Powerfocus is detected but as unrecognized...
Replies
0
Views
67
I am trying to communicate between a 1769-L16 and a beckhoff EL6652 EtherNet/IP-Master. I need 8 INT and 2 REALS. When I generate the eds file, in...
Replies
1
Views
110
Hi everyone: I went to AB.com, found only firmware, no EDs file showing up. i took a pix of device properties of RSLinx. Thanks
Replies
1
Views
100
Back
Top Bottom