Simantic G120C - Setting speed setpoint from keypad

sanger

Member
Join Date
Nov 2005
Location
Toronto
Posts
172
This should be an easy thing but can't seem to figure it out. Want to start/stop the drive from the terminals and set the speed setpoint from the keypad. Don't see a macro to do this. Started with Macro 12 (terminal with analog speed) but not sure how to set the speed setpoint to keypad control.
 
Hi, I can't really say I've seen those particular drives, but most of the ones I've done had a parameter in set-up that would say "Enable external control = 1" and "enable keypad control = 0" or 2 or whatever. So those were available in speed setpoint selection, forward/reverse, start/stop, reset, etc. Maybe this will help, good luck
 
After discussion with technical support is appears that this is not possible with the BOP keypad we are using. It is only possible with an IOP keypad.
 

Similar Topics

Hi All, I have to make a modification in one of our tool to add in some logics to ON and OFF an inverter. The logic being vacuum between certain...
Replies
0
Views
1,693
I have alarm screen where the alarm message is set as "Simple Message View" with Date and Time. I dont know how to change this date and Time in...
Replies
0
Views
1,451
Hi Guys, I have one Seimans Simantic Panel in our plant which otherwise uses only AB, I am trying to replace this with a panelview. My question...
Replies
2
Views
2,237
A salesman told me yesterday the Siemens has stopped producing the 505 series controllers and I/O. They will continue to sell units in stock, but...
Replies
2
Views
3,998
Hello I wanted to ask some questions about the G120C drive and the protection for it. I want to control a pump, with the motor rating of 5.5 kW...
Replies
3
Views
193
Back
Top Bottom