about S7 Communication

amit.khupe

Member
Join Date
Nov 2006
Location
Mumbai
Posts
1
i want to know about S7/H400 PLC communication. which communication are available and if i wants to take that Plc on Industrial Ethernet then how to do that is this required any additional module or in processor onbord ethernet is available i m familler with AB PLC's but not able to find regarding to Simens S&/H400 plc. i have a problem that in my sys config it is shown only profibus and modbus communication so what is the distance limitation for profibus communication PLC to Engg. work station. can any one just help me out
 
Hello amit.khupe;

Both Industrial Ethernet and Profibus-DP/PA are available for S7-400H communications. For both you can use copper or fiber (not for PA of course). The limitations on the numbers of astations for profibus-DP is 31, exceptionnally.
If you want to connect through Profibus-DP to an enginnering station, you can go up to 500 m at 1,5 MB. If you need to maintain fault-tolerant connections, you will need a software called S7-redconnect on your PC to switch connections in case of communication failures.
All this information can be found (with details) in the manual S7-400_e.pdf (Automation system S7-400H Fault0tolerant System) on the Siemens support webpages.
Hope this helps,
Daniel Chartier
 

Similar Topics

Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
30
Hi all I need help on this As in my project used Schneider TM241 controller. Now I want to communicate Elite energy meter with controller by...
Replies
3
Views
89
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
Replies
4
Views
78
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
89
I have an issue on my vessel, we have water tight door system created in China, company is no longer operating. We have 7 doors each with their...
Replies
3
Views
113
Back