SLC 5/03 passthru to Ch0 DF1 to PV300

BillTo

Member
Join Date
Aug 2005
Location
Vancouver
Posts
3
I am trying to link to a PV300 (not micro) that is directly connected to the Ch0 (DF1) port of a SLC 5/03 (OS302). My computer is connected to a DH485 network on Ch1 of the SLC. Intent is to be able to remotely update the Panelview WITHOUT having to direct connect to it.

I 'think' I have the passthru bits set properly in the SLC status file. I can see the SLC within RSLinx v2.42 (RSWho) but I cannot see the Panelview.

Any suggestions or comments as to whether or not this can actually be done?

Thanks.
 
Something to try: In Panelbuilder32's communications setup dialog there is a option check box that says "Use Networking". Set that check box on and re-download the panelbuilder file to the PV300. The default setting is off. Please post if you're successfull or not.
 
Checked the "use networking" & re-downloaded.

Still can't see the PV through the SLC.

I suspect that IF it can be done, it is something with the configuration of RSLinx.

Currently have the PV set to node 1, SLC Ch0 set to node 2
I've seen some stuff on the AB site that mentions that the SLC 5/03 cannot do bridging (see KB # G14044 at AB site).
 
I recall doing what you're trying to do with a 5/03, though it may have been I was connected with my PC to CHO and the Panelview was connected to the DH485 connection CH1 but it was 5-6 years and many projects ago. Sorry I can't recall more details.

This app note in AB's knowledgebase indicates the 5/03 can do df1 to dh485 passthru with the proper level of firmware and version of RSlinx.
 

Similar Topics

hello all. i know this topic has been beaten to death but i am still cant get it to work on my end. i have a 1747-L532E and a panelview standard...
Replies
4
Views
2,660
When arriving at work this morning, I came into a PV1000 with the config screen pulled up and no application. I have no idea what they did. I have...
Replies
4
Views
2,486
Hello, i am trying to connect a slc503 (os302 series c) with a panelview 600 (2711-b6c8)DH+ i have purchased the datalink DL3500 and have ran blue...
Replies
4
Views
3,831
Looking for some help with downloading to a Panelview 1400e via a SLC 5/04 and 1747-SN,B RIO scanner. The 1747-SN,B is configured for racks 0-3...
Replies
2
Views
10,442
I'm trying to read/write to an SLC5 with a ControlLogix L71 V35 plc that fails. The exact same code works on an L82S with V32. Is there a known...
Replies
9
Views
119
Back
Top Bottom