VFD power calculation

rQx

Lifetime Supporting Member
Join Date
Oct 2010
Location
Trelleborg
Posts
1,051
Hi,

I have a VFD from wich I cannot read the power output. However I can read the current and voltage.
Am I correct to say that this formula will give me the power consumption of my VFD? Or do I need something more?

P=√3*U*I

/Tim
 
In any case, this formula will give you the Apparent Power in VA (VoltAmper) but not the Active Power in W (Watt) which is the one that really consumes energy
 
Tim, hi. You can use V x A x 1.73 x PF / 1000 and you will get KW. However one must know the power factor. Usually it is around .8 or .9 lagging if it is a good power factor. Hope this helps.
 
Tim, hi. You can use V x A x 1.73 x PF / 1000 and you will get KW. However one must know the power factor. Usually it is around .8 or .9 lagging if it is a good power factor. Hope this helps.

.8 or .9 if working at nominal power but .1 or less if running idle without load
 
Thanks for all the help. It then seems impossible to get the power out of this drive, it has a register for power on the modbus side but it doesn't seem to work. I'll try to investigate some more about why the modbus register don't work
 
Thanks for all the help. It then seems impossible to get the power out of this drive, it has a register for power on the modbus side but it doesn't seem to work. I'll try to investigate some more about why the modbus register don't work

What is the problem with that register, always contains zero?
 
It is a Parker AC10. It has been a while since I played with it so I don't know the exact reason why I concluded that it didn't work. I will try to test on friday what results I got, maybe they have updated the firmware also
 
Sometimes the power output is provided as a percentage of the rated motor power that you enter into the drive.

I have done what you're doing (using volts, amps and pf) with a VSD before and the results were +- 10% at best. That was with Schneider ATV61.

That calc also doesn't take into account power consumed by the drive itself.
 
I want to meassure the active power, the one I pay for. We will run a pump with a PID control at diffrent pressure and want to know how mush power it consumes at diffrent settings.
 
The register that say "read integer power value" returns zero when the motor is running. But then again I maybe dont fully understand what the register should return or mean. There is also "percentage of output torque" that also return zerio. Maybe these values are nor active when I run v/hz
 
For "read integer power value" I understand the integer part of the power, maybe in kW? maybe there is another register with the fractional part.

In your tests the motor runs with load or runs free without load?

If it turns free the active power will be very low, close to zero.
 

Similar Topics

I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
107
We have a devicenet consisting of 15 PF755 drives in a centerline MCC, and on a separate trunk cable coming off the scanner, a single PF525 in a...
Replies
0
Views
332
I need small power supply that has very small ripple and 250VDC for my workshop. I came to idea to use DC bus from VFD that has 3x230VAC output as...
Replies
6
Views
2,092
A little background at my complex we run power flex 755 VFD's 480V most of them are 361 Amp. They are etherneted to a controller the VFD has a...
Replies
1
Views
5,400
I am using power flex 700 VFD. and motor is in open loop mode but continuesly break slip fault error show in drive display .
Replies
2
Views
1,339
Back
Top Bottom