Old March 16th, 2023, 03:11 PM   #1
Slwagner73
Lifetime Supporting Member
United States

Slwagner73 is offline
 
Join Date: May 2017
Location: Bellevue, MI
Posts: 52
755 Over amping

Gents:

Quick rundown.

Water pump, 75ft of head pressure on a 10” line, open at the discharge end to a pond. (Per customer).

755 75hp 480VAC 3ph.
75hp 230/460 motor, 170/85.1 amp, 1775 rpm.

I ran the setup wizard for this, did the usual rotation check, and then did the static tune. Every thing came out just fine, and the pump starts and runs like it should, amps match hz’s, everything looks good until you go above 40hz.
Then the amps really climb, going way over 110 amps at 50hz. At which point it faults on overcurrent. That’s kind of a no-brainer, it’s doing what it should.
Long story short, I have no idea what could cause this.
The pump is belt driven, the discharge valve is wide open, and the check valve “appears” to be functioning.

This pump ran fine at 30-35hz for a week, but now they want to ramp it up higher, and like I stated, you see the results.

Now I’m stumped.
  Reply With Quote
Old March 17th, 2023, 08:15 AM   #2
DarrylR
Member
United States

DarrylR is offline
 
Join Date: Nov 2019
Location: illinois
Posts: 82
Looks to me you may have an undersized drive. 75hp @480vac is rated for 96 amps. 100/125hp @480vac are good for 124/156 amps.
  Reply With Quote
Old March 17th, 2023, 09:58 AM   #3
g.mccormick
Lifetime Supporting Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 901
Is the motor wired correctly for the voltage? I had similar issue before on a centrifugal pump. The VFD was 480 and configured for 480. The motor got wired for 230V instead of 460V. As the speed and power increased (centrifugal pump variable torque load) the current would go through the roof.
  Reply With Quote
Old March 17th, 2023, 10:02 AM   #4
g.mccormick
Lifetime Supporting Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 901
Here is my thread from a few years ago from my issue. Sounds almost exactly the same as yours.

http://www.plctalk.net/qanda/showthread.php?t=125669
  Reply With Quote
Old March 17th, 2023, 02:37 PM   #5
jaden
Member
United States

jaden is offline
 
Join Date: Sep 2009
Location: Pleasant Dale, Nebraska
Posts: 280
Centrifugal pumps work on the "Laws of Affinity", which means the Torque goes up as the square of the speed difference, and Horsepower goes up as the cube of speed variation. Ex., if you double the speed of a pump, the torque will be 4 times , and the HP eight times.
  Reply With Quote
Old March 17th, 2023, 02:48 PM   #6
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,124
Quote:
Originally Posted by jaden View Post
Centrifugal pumps work on the "Laws of Affinity", which means the Torque goes up as the square of the speed difference, and Horsepower goes up as the cube of speed variation. Ex., if you double the speed of a pump, the torque will be 4 times , and the HP eight times.
To further this concept;
In a centrifugal pump, load = flow. So if the discharge is "wide open", it may be that the pump and motor were selected in such a way (by the mechanical engineer, if any) for a flow rate that was NOT supposed to ever be "wide open" on the discharge end. So as mentioned, the pump may be too small for any more flow than you can get at 40Hz. That's a mechanical issue, not an electrical one.

Last edited by jraef; March 17th, 2023 at 02:50 PM.
  Reply With Quote
Old March 19th, 2023, 08:47 AM   #7
Slwagner73
Lifetime Supporting Member
United States

Slwagner73 is offline
 
Join Date: May 2017
Location: Bellevue, MI
Posts: 52
Thank you all for your answers.
So, here is the update:


I checked the motor for correct wiring. And it is correct.
The drive is sized for the motor, i.e. HP is correct, Amps are correct, so I can't find any issue there.
The setup is the same as the two existing pumps, except they are on contactors, so the amp draw on them matches the nameplates of those moors. Ergo, I don't believe it's an engineering issue.
I am still at a loss...


Thanks:
Scott:
  Reply With Quote
Old March 19th, 2023, 09:51 AM   #8
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 6,253
You need to plot two curves together:

Start with the pump curve. Ideally, it should show performance at multiple speeds. On it plot the designer's system curve head vs. flow. his may be a horizontal line at 75 ft if the head was considered constant.

Then plot the actual system curve. This will be a parabola with a non-zero intercept. The intercept will be the actual static head. The parabola is the friction loss and Δh = k q²
You can use the actual head measured at any measured flow to calculate k.

h total = h static + Δh

Once you've done that you will have a handle on the actual hydraulic performance and the original design performance. Then you can eliminate or confirm the pump and hydraulic system as the source of your problems.

https://www.linkedin.com/pulse/apply...tzAFYldQ%3D%3D
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
powerflex 755 Fallo de giro - Problema con el Giro en Powerflex 755 edgexzw LIVE PLC Questions And Answers 7 October 31st, 2022 10:11 PM
AB Powerflex 755 drive PID control questions Nan LIVE PLC Questions And Answers 1 September 18th, 2020 10:06 PM
Powerflex 755 Fault 5 Overvoltage mort81 LIVE PLC Questions And Answers 3 October 14th, 2019 03:25 PM
Powerflex 755 rev 10.02 not showing in rslogix 5000 rev 20.01 edwardeduful LIVE PLC Questions And Answers 6 November 30th, 2017 01:12 PM
Powerflex 755 not outputting over motor nameplate current remlapw LIVE PLC Questions And Answers 3 January 20th, 2017 11:03 AM