plc storereviewsdownloads
Reply
Thread Tools Display Modes
Old March 9th, 2023, 03:38 PM   #1
the_msp
United Kingdom
the_msp is offline
the_msp's Avatar
Comms to FX3U
Looking at getting comms to an FX3U to Ignition. There is already an expansion card left of the PLC giving Ethernet.
I am using Ignition Edge Panel so don't want an HMI with drivers.
Looking at the DataStation from Red Lion DSPLE000.
I see in the drivers list it has these for Mitsi:
Quote:
A/Q/FX Series TCP/IP MasterEthernetYY A/Q/FX Series UDP/IP MasterEthernetYY FX2N Encapsulated TCP/IP MasterEthernetYY Q Series TCP/IP MasterEthernetYY A/Q/FX Series - MELSECSerialYY FX SeriesSerialYY MELSEC 4 SlaveSerialYY MELSERVOSerialYY
I was going to add an MB3170 to convert Modbus RTU to TCP as well, but if the data station can do that on RS485 2-wire then all the better. The moxa is almost £300 now, online price for DSPLE is £635 so if I can do away with the moxa then the DSP is quite reasonably priced.
__________________
Regards,
Patrick G. B.Eng MIET
Making the flashy lights flash since the 90's
SCADA - Inductive Automation Gold Integrator | PLC | Control Panels | Robotics | Training
Connect with Matrix Engineering
My son was chewing on an electrical cord, so I had to ground him. He is doing better currently and conducting himself properly. My electrical skills are quite poor, which is a shock to some people
Old March 9th, 2023, 11:36 PM   #2
pesedo77
Banned User
Alderney
pesedo77 is offline
Old March 10th, 2023, 02:19 AM   #3
parky
United Kingdom
parky is offline
parky's Avatar
The adapter card (left hand side) that plugs into the PLC is different to the Enet card that fits in the I/O bus on the right, never used the adapter & I know it is limited, the usual connection is to use the programming protocol "Melsec Connection" The redlion data station should have a driver for this as I expect it is the same protocol as the serial 422 port but encapsulated.
If using the 422 programming port then be aware that many HMI's or other communication units have to be set at 9600, The FX defaults to that on power up, I know that Beijers HMI's like GXDev & Works can force the baud rate I believe it tries all rates to connect & then forces the FX to the rate the HMI is set to, I used kepware with ethernet encapsulation to a Ethernet to 422 converter to get data from a FX3U, It worked at 115kb but I noticed after a day it stopped communicating, went on-line with GXWorks at 115 kb & when I connected the ethernet converter it started working, eventually realised that providing the FX is not powered down it will stay at the rate you set it at but defaults to 9600 on power down/up. Kepware is not capable of auto change of the baud rate & it is possible other HMI's or software may not be able to, many years ago I had a proface that only seemed to work at 9600.
If you do not need high speed coms then 9600 would be fine, I would expect most HMI's will have some form of coms for Melsec connection via the Ethernet adapter.
If using ModBus then I believe you will need a card with the MB sufix, this goes for the 232/422 interface cards as well.
Old March 15th, 2023, 06:59 PM   #4
the_msp
United Kingdom
the_msp is offline
the_msp's Avatar
Thanks Parky. I reached out to my local red lion distributor and he advised that the DSPLE is active mature and perhaps not the best choice now. It has been superseded by Flexedge DA50A. Both units should talk to the Mitsi comms card on left (think it's called ADP maybe).
The modbus is only for talking to danfoss soft starts.
__________________
Regards,
Old March 16th, 2023, 03:03 AM   #5
parky
United Kingdom
parky is offline
parky's Avatar
Here is a link to the manual
https://eu-assets.contentstack.com/v...97D45801-F.pdf
Old March 16th, 2023, 03:37 AM   #6
goghie
Serbia
goghie is offline
1. FX-ENET-ADP has very limited options.
2. FX-ENET-502 is intended for Modbus TCP/IP
3. FX-ENET is with all capabilities and it supports Modbus if you install libraries or you make your own code for it. Libraries are available free of charge. It supports up to 8 simultaneous connections, email, etc. (I use only this one)
If your panel supports Melsoft/MC protocol, you can use any ENET card.
Old March 16th, 2023, 03:47 AM   #7
parky
United Kingdom
parky is offline
parky's Avatar
Goghie is right, the ADP does not have MB, there is a card like Goghie says that fits on the right that is MB compatible but the standard is not so you would need to write some code never used the libraries for MB so cannot comment on how good/easy they are, the ENET card is definitely the one to go for far more options like MB, MC Protocol, Melsec connection etc.
This is the one I have always used.
Old March 16th, 2023, 03:02 PM   #8
the_msp
United Kingdom
the_msp is offline
the_msp's Avatar
Sorry I didn't clarify enough, the modbus is for Ignition->Danfoss comms only. The PLC does not need to know or control status of the danfoss over Modbus. That will be hard wired.
When I get some time I will download Crimson and ensure it can do Melsoft/MC protocol.
Thanks all.
__________________
Regards,
Old March 17th, 2023, 04:01 AM   #9
parky
United Kingdom
parky is offline
parky's Avatar
Just had a look at Crimson, never used it but it looks like it has the Drivers for the FX range both 232 & ethernet, I noticed if you load the UDP driver the ports are in the 5000 range this is what I have used on Kepware so it looks like it has the drivers required.
Old March 19th, 2023, 02:39 PM   #10
the_msp
United Kingdom
the_msp is offline
the_msp's Avatar
Calling a mod with a banning stick. Would advise no one to click the links above.
__________________
Regards,
Reply
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
L33ER CompactLogix V31 comms Issue sjames LIVE PLC Questions And Answers 5 January 12th, 2022 02:28 AM
RS 232 comms eebads2391 LIVE PLC Questions And Answers 6 April 12th, 2021 08:36 PM
[ControlLogix] Weird timeout on 1756-ENBT when comms lost to any remote PLC defcon.klaxon LIVE PLC Questions And Answers 4 August 5th, 2016 03:13 PM
[Logix] Intermittent comms issue (ethernet/ip) between Control and Compact Logix PLCs defcon.klaxon LIVE PLC Questions And Answers 19 February 4th, 2016 05:00 PM
Mitsubishi Comms burnerman LIVE PLC Questions And Answers 4 October 16th, 2008 05:26 PM