Kepware routing help
Kepware rookie...
For some OEE purposes, we are trying to collect data from a ControlLogix PLC. We have to go thru an another ControlLogix backplane to get there. We keep getting "invalid device id" errors. Is it possible? Is our format wrong? The path we set is: <10.1.ww.yy>. 1. 2. 2 <192.168.xx.zz>. 1. 0 10.1.ww.yy is an EWEB card, to the backplane, out the ENET card in slot 2, to the other PLC. Seems right. Maybe not... Thanks Justin |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
It looks essentially correct to me.
There should be a "." before the second IP address (but I assume you typed this out instead of copy/paste/edit). Remember that ControlLogix slots start at the leftmost Slot 0. This assumes that your second Ethernet module is in the third physical slot (2) of its chassis, and that the target ControlLogix CPU is in the first physical slot (0) if its chassis. Have you been able to navigate the same path with RSLinx Classic and maybe set up an OPC Topic, and use the Test Client ? |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Mar 2011
Location: Drinking in Wisconsin
Posts: 56
|
Yep, that path was typed out. I forgot the "."
I can drill down to the processor thru Linx. Next question is DH+. The same 10.1 chassis has DH+ cards. Any pointers on what the format thru the backplane and out a DH+ card would look like? |
![]() |
![]() |
#4 |
Lifetime Supporting Member + Moderator
|
Unfortunately I'm not sure how Kepware navigates the 1756-DHRIO.
MSG instructions from PLC's are aimed at the DHRIO itself with a payload that says "execute a PCCC/DH+ command on this Channel, with this target node/gateway node/link ID, and give me the result". There's no CIP path that includes the channel/node/gateway/linkID. RSLinx Classic basically does that behind the scenes and shows it in a graphical browse. So this might be a Kepware-specific configuration question that I can't answer. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Kepware and RSView Studio 5000 | martinshaw | LIVE PLC Questions And Answers | 10 | July 18th, 2019 12:56 PM |
cimplicity V9.0 talking to remote Kepware OPC server | dogyi | LIVE PLC Questions And Answers | 1 | March 4th, 2016 12:23 AM |
BACnet communication between Kepware communication server 5.8 and BACnet Card. | lalitvedak | LIVE PLC Questions And Answers | 0 | December 23rd, 2012 12:03 AM |
Change RACK ID on Kepware dynamically !! | amitgolwala | LIVE PLC Questions And Answers | 1 | June 30th, 2011 09:19 PM |
Siemens STARTER and routing ethernet / profibus. | JesperMP | LIVE PLC Questions And Answers | 2 | April 29th, 2010 09:15 AM |