OT: CT transducer

the_msp

Lifetime Supporting Member
Join Date
May 2008
Location
Northern Ireland
Posts
1,271
I have a set of these:

https://www.i-s.gr/files/ND Clamp-on CT Brochure.pdf

Specifically M1.UM which outputs Voltage.

I am looking to use these Monday for some test measurements into a PQA however it only takes 1A or 5A Current inputs.

Are there any transducers available that will scale this for me?

I have one Rogowski coil here that will sort of let me away, but ideally I'd like 3 phase. My local supplier has no more Rogowskis' in stock right now.

Space is too limited for standard Open-coil CTs.
 
Something like this is close:

http://www.sil.co.uk/pdf/dtm3u.pdf

The load I'm measuring is motor FLC at 80A, but currently star-delta so a peak inrush is expected.

The PQA is a Janitza 512 Pro, and whilst I've only ever used 1A or 5A input, in the software it lets you select mA.... hmmm...
 

Similar Topics

Hi all, I have a AC current transducer that I want to bench test to ensure I am getting a 4-20mA output. I am using a AE001 unit. It is very...
Replies
4
Views
115
Good morning everybody, I hope you are very well. I share with you the information of the PLC LOGO! Siemens and expansions that we have...
Replies
4
Views
1,077
Has any used a ballistic pressure transducer with a PLC? I am not sure if it will capture the event that I need to use as a control. The device...
Replies
2
Views
1,075
I am updating controls on a leak tester, from a SLC 5/02 to Compact Logix. The SLC used a DDV instruction to help scale a differential pressure...
Replies
17
Views
4,402
I have a Pump 1 Current in my Local:5:I.Ch00Data address. I need to add this to my ladder logic program as the goal is to have it eventually be a...
Replies
2
Views
1,466
Back
Top Bottom