PF525 reset

mavrick

Member
Join Date
Jun 2015
Location
usa
Posts
122
I'm using a powerflex 525 drive communicating over Ethernet.
I'm having to cycle power if I have a fault such as Ethernet loss or if the building losses power and then the drive powers back up. Is this typical? I have looked through manual and I thought there was a parameter that will allow you to reset faults from the red button on the drive keypad. Thanks
 
Parameters C125 (Comm Loss Action), C143(EN Comm Fault Action) and C144 (EN Idle Fault Action) will change the comm fault action in the drive.

I kind of remember you could just have the drive fault and reset it from the PLC but don't have the parameters around me.
 