Need help With Omron C200H AD001 AI

Join Date
Mar 2004
Posts
55
I have an AD001 Analog Input card in an Omron rack with a C200H CPU. The card is in slot zero. I'm using a PRO15 to program the CPU. All I want to do is verify if the module is working. I've cleared the I/O and verified the configuration. I've entered an end statement.

What I don't know how to do is monitor the inputs. I think the address starts with IR101.

Is there anyone who has experience with this setup. Again, all I want to do is input a voltage signal and verify that the CPU is receiving data from the monitor.

thanks,

CTG
 
The card is not addressed in the slot it sits in. Rather the card gets its starting address from the "machine no" on the front of the module.

If the Machine No is 0, then it is addressed at IR100-IR109. The first input word will be IR101. Also the switches are read at power on and not after, so if you change the machine no, you will need to cycle the power.
 

Similar Topics

I have a question about SET instruction in Cx-programmer. When condition goes true it is supposed to give value 1. But, my controller is giving 0...
Replies
24
Views
2,245
Hi, I don't have any formal education background with PLC. I am learning PLC by myself. I have CJ2M CPU34 unit and CJ1W-DA021 unit. I would...
Replies
1
Views
1,215
Hey all, I am working on this new project where i am devloping hmi in cx desiner , i have one question if i want a screen which only shows on...
Replies
2
Views
1,714
hello guys I'm having problem in pid in Omron cp1l plc I have program . I'm getting alarm when I execute pid
Replies
1
Views
2,799
Good day all, Newbie here so I'm practising my posting skills. I have a problem with one of the Omron C200HG PLC''s in our plant. This particular...
Replies
0
Views
1,456
Back
Top Bottom